Is there anyone with some input on framing an intersecting unequal pitch roof. I want to have both ridges pretty much in line with each other. The major roof is a 5/12 with a total run of 14'-3 5/8" and a total rise of 5'-11 1/2". The minor roof will have a total run of 9'-2 1/4". Thanks.
Do both roofs have ceiling joists or either one cathedral ceilings?
Thanks for your reply.
Main roof will have 2 x 8 rafters with 2 x 10 ridge and will bear on 2 x 4 plate on ceiling joists on existing 2 x 4 walls.
Minor roof (which is an addition) will have 2 x 6 rafters with 2 x 8 ridge bearing on 2 x 4 plate on top of ceiling joists on 2 x 6 walls.
Projection will be 16" including the shingles (The dimensions given include my overhang.)
To the best of my knowledge, I need to raise the addition wall height 3 3/4 " more than existing walls to have fascia and shingles line up. If I use the same total rise for the minor roof' where does that actually put my minor ridge in relation to the major ridge? It shouldn't be 3 3/4" higher?
This is the part I'm having trouble visualizing.
You can have the same pitch for both roofs. The only thing different would be the LCR of the 2 roofs, I know the LCR formula is rise squared, run squared then get get the square root. In your case: 5 squared plus 12 squared is 169. And the LCR is 13. then take 13 and multiply it by the run which is 9.1875. And the theoretical LCR would be 109.4375''. But then you need the O.H(over hang) you want to add it to the LCR. Which is O.H divided by 12, multiplied by the LCR.
The 2 roofs should be the same pitch. The rafters just change size.
Eeek, it says you have two different slopes. Sorry, the information I just wrote doesnt have to do with anything. I read the topic different.
Here are the trwo drawings. One is the cross section of the two roofs showing the relationship between the ridge height with both ruins and the outside pint of the 15-1/4" overhang. You always figure the length of the overhang to get the exact pitch and exact rise. Notice that doing this creates a triangle giving you the run and rise of both pitches.
The second drawing is a close-up of the outside points at the fascia where the two pitches meet perfect. The overhang run and rise shows you at the plate-line the difference in plate heights using a 2x6 and 2x8 with a full 3-1/2" seatcut.
OK, this makes it clear now. One thing though...given your dimensions on your drawing, it seems I need to clarify myself. The dimensions I gave were the total run including the projection of 15 1/4" to outside of fascia and 3/4" for the shingle projection past the fascia. So I come up with a total rise of 5' 11 1/2". I see you took my total run dimensions to the end of the wall and calculated a different total rise. My difference in wall heights of 3 3/4" was calculated accordingly:
total projection/total run of common (minor) x total rise
SUBTRACT
total projection/total run of common (major) x total rise
16"/110.25" x 71.508" = 10.37757823
SUBTRACT
16"/171.625" x 71.508" = 6.666441369
= 3.711136861 or 3 11/16"
Please tell me your take on this, I'd appreciate it.