Old 04-22-2010, 06:09 PM   #1
load-bearing or non load-bearing wall?
Hi,
I have a little reno project going on right now. I am just about to take a wall down and still wondering if it is load-bearing or not. I had the opinion of two contractors already but they disagreed on the matter... The fact is that the framing shows characteristics of both a load-bearing and non load-bearing wall.
Here is what you need to know:
- 8' partition wall between kitchen and living room, located on first floor (unfinished basement below)
- Runs perpendicular to the joists and trusses
- No point of contact with trusses in the attic (meaning that the web doesn't sit directly on the top plate, offset by a foot or so)
- Also offset with footing in the basement (main beam in the basement is aligned with the footing)
- Double top plate, 2X4
- Had a pocket door (now removed)
- Header above pocket door is a 2X4 on the flat with criple studs (no beam or plywood)
- Trimer studs are present and made of finger-jointed studs (vertical use only)
Can you help?
Cheers,
dgsquare
dgsquare is offline   Reply With Quote
Old 04-22-2010, 06:14 PM   #2
truss above probably nonbearing right there
The older I get the better I was
Old 04-22-2010, 06:18 PM   #3
Moderator
kwikfishron's Avatar
I would say it’s not load bearing. Full span trusses are designed to be bearing on the outside walls. If it was load bearing that should be a solid and not a box header.
-NEW MEMBERS-
Please include your basic location in your profile. Some of the answers given are specific to a Region or State.
kwikfishron is online now   Reply With Quote
Old 04-22-2010, 06:21 PM   #4
It was a dark and stormy
Yoyizit's Avatar
Stretch a level line at right angles to the partition as close to the ceiling as possible.
A non load bearing partition will have the max. ceiling sag in the middle of the ceiling span. A load bearing partition will be raising the ceiling slightly.
In a 10' span you might be looking for a sag of 3/8".
That single horiz. 2x4x5' laying on its flat side above the opening can't bear much load, if that is its purpose. See how much sag it has in the middle. 0.1" sag means its carrying about 0.6# per inch of length, unless it is already warped.
It's like having a built-in strain gage.
Using Excel prevents math mistakes \/
b= 3.5 >enter value
h= 1.5 >enter value
I= 0.984375 =calc'd value
E= 1000000 >enter value
d= 0.1 >enter value
L= 60 >enter value
w = d384EI/5(L^4)
d384EI= 37800000 =calc'd value
5(L^4)= 64800000 =calc'd value
w= 0.583333333 =calc'd value
Old 04-22-2010, 06:22 PM   #5
agree with tpolk... from info you provide..
a pic from top side would confirm your statements...cheaper than an Engr...
Big Bob is offline   Reply With Quote
Old 04-22-2010, 06:59 PM   #6
Thanks for the quick replies.
Here is more info and a couple of pics from the attic. In the first picture, you see the 2X4 that makes up the top plate of the wall, and you can clearly see that there is no contact point with the web. In the second picture you see a little bit more of the trusses, again with the 2X4 that makes up the top plate of the wall (to the right completely).
@kwikfishron, I agree with you that the header should be solid or at least strengthened with plywood to make it load bearing.
@Yoyizit, the 2X4X5' that makes the bottom part of the header is sagging a little (no more than a 1/4"), with the lowest point in the middle. I think this is due to the fact that trimers are found below that 2X4 on each side but not above it. It is definitely not designed to support a load. I still have to do the level line exercise to see if the whole ceiling is sagging.
Old 04-22-2010, 07:07 PM   #7
Moderator
If that walls in your way, get rid of it.
-NEW MEMBERS-
Old 04-22-2010, 07:48 PM   #8
Originally Posted by kwikfishron View Post
if that walls in your way, get rid of it.
have at it ! Totally agree...
Old 04-22-2010, 10:25 PM   #9
Goin' down!
Thanks,
dgsquare
how to-create doorway in load bearing wall Nikkil Building & Construction 4 05-14-2011 12:31 AM
Sister joist and load bearing wall Daniel048225 Building & Construction 2 09-21-2009 10:33 PM
Is this Load Bearing Wall remodel-virgin Building & Construction 16 05-11-2009 05:25 PM
Raising Doorway Height (load bearing?) treefrog Building & Construction 6 02-25-2008 10:11 PM
Load Bearing Wall rpatterson Building & Construction 2 10-29-2005 08:43 AM