-   -   External intake and exhaust vents (http://www.diychatroom.com/f19/external-intake-exhaust-vents-47155/)
monkeysee 06-21-2009 12:43 PM
I want to install a couple of vents but my neighbor's wall is within 3 feet of these vents (directly facing)....is it okay to go ahead or is it against the building code? thanks for any information that you can give me.
Ron6519 06-21-2009 04:51 PM
It would help if you stated what you were venting and where you're located as what can be done is sometimes regulated differently from place to place. If this is a condo, there are even more regulations.
Ron
monkeysee 06-21-2009 05:29 PM
Ron
Thank you so much for replying so quickly. One is a dryer vent and the other is for the washroom. This is not a condo but a house. I realize that every regulations differ but is there any sort of general consensus regarding this.
Thanks.
Gary in WA 06-21-2009 10:27 PM
Bath fan- duct termination min. 3' from bldg. openings or plate line. IRC 302.2 UBC 504.5
Back-draft damper required.
Clothes dryer- duct termination- End outside in back-draft damper& no screens
Min. 3' from other building openings UBC 504.5 Smooth metal inside. No screws in airflow. 4" min. duct.
25' minus 2' per 45* bend, 5' per 90*. Male ends must face direction of airflow.
Steel duct only through fire-rated assembly. Be safe, G
monkeysee 06-22-2009 08:27 AM
Thanks, the information that you provided really helps.