I'm planning to add on a 12' by 26' room addition to the end of my house going out over the driveway. I will be spanning the entire width of the driveway with a 26' steel beam. There can't be any supports in the middle of the beam because of the drive, and the beam can only be 12" tall for vehicle clearance. It is a gable end, so the beam will not be supporting much roof load. What size beam should I go with?

Advertisement

jjohnson112 is offline   Reply With Quote
Old 01-11-2011, 04:12 PM   #2
Experienced
 
Jackofall1's Avatar
 
Join Date: Dec 2010
Location: Southern Michigan
Posts: 2,822
Rewards Points: 2,000
Default

26' Steel I Beam


If the beam is at the bottom it is supporting a minimum of 1/2 of the total load, which will include the roof.

Where do you live?

What is holding up the rest of the addition ie outside walls?

What type soil for foundation?

Even with these answered you will definately require an engineer to survey the site and do total load calculations.

I could tell you what size beam, but that is only a small part of the picture. What about posts and foundations.

Advertisement

__________________
When its all said and done there is usually more said than done
Jackofall1 is offline   Reply With Quote
Old 01-11-2011, 05:01 PM   #3
Retired from the grind
 
gregzoll's Avatar
 
Join Date: Dec 2006
Location: Midwest - Central Illinois
Posts: 14,400
Rewards Points: 2,462
Default

26' Steel I Beam


Quote:
Originally Posted by jjohnson112 View Post
I'm planning to add on a 12' by 26' room addition to the end of my house going out over the driveway. I will be spanning the entire width of the driveway with a 26' steel beam. There can't be any supports in the middle of the beam because of the drive, and the beam can only be 12" tall for vehicle clearance. It is a gable end, so the beam will not be supporting much roof load. What size beam should I go with?
What did the arcitect & structural engineer state on the plans that they drew up if they have?
gregzoll is offline   Reply With Quote
Old 01-11-2011, 05:36 PM   #4
DIY Hack
 
Mr Chips's Avatar
 
Join Date: Mar 2008
Location: Location, Location
Posts: 1,302
Rewards Points: 500
Default

26' Steel I Beam


Quote:
Originally Posted by Jackofall1 View Post
I could tell you what size beam, but that is only a small part of the picture. What about posts and foundations.
then why not just answer the question? Would it be so difficult to say something like " the minimum size is X", but this will vary based on factors such as snow load, wind load, foundation, blah, blah, blah....

Quote:
Originally Posted by gregzoll View Post
What did the arcitect & structural engineer state on the plans that they drew up if they have?
they told him they have no idea, go consult the annoymous internet experts. Maybe the guy is just trying to work out a rough materials list to see if he can afford the project before he spends the money to have plans drawn up.

Geez guys, it's his first post, he's asking a pretty specific question, if you don't want to help, don't, but you don't need to jump all over every poster that you believe is going to do unpermitted work from plans he sketched up on the back of a budwieser coaster
__________________
Those who can, do...
Those who can't criticize on the internet
Mr Chips is offline   Reply With Quote
Old 01-11-2011, 05:51 PM   #5
nap
You talking to me?
 
nap's Avatar
 
Join Date: Dec 2007
Location: sw mi
Posts: 5,407
Rewards Points: 2,000
Default

26' Steel I Beam


the problem is;

there is no; it's a beam this big and this thick.

It varies with every question asked and the inference with gregzoll's post is:

You need an engineer to determine this for you using all the variables involved.
nap is offline   Reply With Quote
Old 01-11-2011, 06:19 PM   #6
DIY Hack
 
Mr Chips's Avatar
 
Join Date: Mar 2008
Location: Location, Location
Posts: 1,302
Rewards Points: 500
Default

26' Steel I Beam


Quote:
Originally Posted by nap View Post
It varies with every question asked and the inference with gregzoll's post is:

You need an engineer to determine this for you using all the variables involved.
I understand that. But isn't your response a better answer to give a brand new member asking his very first question?maybe i'm just having a bad day, but it seems the first answer was" i can tell you but i won't" and the second seemed passive-aggressive.

it seems like a growing trend of this site is to ridicule those brave enough to ask questions
__________________
Those who can, do...
Those who can't criticize on the internet
Mr Chips is offline   Reply With Quote
Old 01-11-2011, 06:25 PM   #7
Retired from the grind
 
gregzoll's Avatar
 
Join Date: Dec 2006
Location: Midwest - Central Illinois
Posts: 14,400
Rewards Points: 2,462
Default

26' Steel I Beam


Quote:
Originally Posted by Mr Chips

I understand that. But isn't your response a better answer to give a brand new member asking his very first question. maybe i'm just having a bad day, but the first answer was i can tell you but i won't and the second seemed passive-aggressive.

it seems like a growing trend of this site is to ridicule those brave enough to ask questions
It is about liability. If a person was to give a answer without knowing all of the variables involved, and Bubba decided that was correct, whuch it is not, the responsibility falls back on the person who answered with improper information.

In other words, no one wants to claim this responsibility when bubba goes out and orders said I beam, then their house falls in. At that point all parties become responsible for bad information, and unsafe practices.

Engineering something like this, is not something that some Joe on the Internet can answer.
__________________
Ren: Now listen, Cadet. I've got a job for you. See this button? Ren: Don't touch it! It's the History Eraser button, you fool! Stimpy: So what'll happen? Ren: That's just it. We don't know. Maybe something bad, maybe something good. I guess we'll never know, 'cause you're going to guard it. You won't touch it, will you?

Last edited by gregzoll; 01-11-2011 at 06:28 PM.
gregzoll is offline   Reply With Quote
Old 01-11-2011, 06:28 PM   #8
the Musigician
 
DangerMouse's Avatar
 
Join Date: Jul 2008
Location: I'm right here!
Posts: 10,404
Rewards Points: 2,000
Default

26' Steel I Beam


Once again, this is a public forum. When anyone posts a question, they can expect to receive any type of answer from anyone out there.
As moderators, we try to keep the negative comments to a minimum, but it's not always possible to catch them all. If you see anyone being rude or insulting, etc., please just report them so we can do our jobs and continue to make this a fun, friendly, family-oriented forum.

Thanks Guys!

DM
__________________
[SIGPIC][/SIGPIC]Click here to see some of my original magic tricks and trick boxes!
DangerMouse is offline   Reply With Quote
Old 01-11-2011, 06:31 PM   #9
Framing Contractor
 
Join Date: Apr 2006
Location: Caldwell, NJ
Posts: 1,758
Rewards Points: 1,000
Default

26' Steel I Beam


Quote:
Originally Posted by Mr Chips View Post
I understand that. But isn't your response a better answer to give a brand new member asking his very first question?maybe i'm just having a bad day, but it seems the first answer was" i can tell you but i won't" and the second seemed passive-aggressive.

it seems like a growing trend of this site is to ridicule those brave enough to ask questions
The growing trend on this site is that people ask an impossible question that cannot be answered like what size beam to use for a 26' span on the internet and people are dumb enough to give sizes out with such a big beam. None here can possibly answer that question. The best advise and safest advise is to recommend to the poster to have a professional give them the size because.....a professional IS the only one who can give them the size beam to use, NOT someone on the internet......it's that simple.

I don't care what you say, no one here can answer what size beam this guy needs.

Quote:
Geez guys, it's his first post, he's asking a pretty specific question, if you don't want to help, don't, but you don't need to jump all over every poster that you believe is going to do unpermitted work from plans he sketched up on the back of a budwieser coaster
90% of the time it's true. When you ask them about permits and inspections some say they are not getting them and the others never come back.

Why don't we let the OP come back and tell us that he is having plans drawn up for this because he certainly HAS to. The person who does draw the plans will give him the size. If he doesn't need an architect or engineer to draw plans for the permits and inspections, a beam this size should be spec'd by one for him. Where I';m from you don't need an architect or engineer to draw plans for the town. A homeowner can draw the plans, but they have to be approved by the town.

OP are you having plans drawn up and getting permits and inspections ?
__________________
Joe Carola

Last edited by Joe Carola; 01-11-2011 at 06:46 PM.
Joe Carola is offline   Reply With Quote
Old 01-11-2011, 06:33 PM   #10
DIY Hack
 
Mr Chips's Avatar
 
Join Date: Mar 2008
Location: Location, Location
Posts: 1,302
Rewards Points: 500
Default

26' Steel I Beam


Quote:
Originally Posted by gregzoll View Post
, no one wants to claim this responsibility when bubba goes out and orders said I beam, then their house falls in. At that poimt all parties become responsuble for bad information, and unsafe practices.

Engineering somethimg like tgis, is not something that some Joe on the Internet can answer.
That's my point. isn't that response, or none at all better than thread-crapping the guy? it just seems to be done way too often here. Personally I'd rather get no answer than " what size did the engineer who drew up the plans spec"
__________________
Those who can, do...
Those who can't criticize on the internet
Mr Chips is offline   Reply With Quote
Old 01-11-2011, 07:03 PM   #11
Retired from the grind
 
gregzoll's Avatar
 
Join Date: Dec 2006
Location: Midwest - Central Illinois
Posts: 14,400
Rewards Points: 2,462
Default

26' Steel I Beam


Quote:
Originally Posted by Mr Chips View Post
That's my point. isn't that response, or none at all better than thread-crapping the guy? it just seems to be done way too often here. Personally I'd rather get no answer than " what size did the engineer who drew up the plans spec"
Because if no answer is given, then you hear all over other sites that such and such site is hard to get answers from. Majority of these posts that I have seen in the past couple of weeks are drive by's and a lot them are posted the same way on various other sites on the Internet.
gregzoll is offline   Reply With Quote
Old 01-11-2011, 07:21 PM   #12
DIY Hack
 
Mr Chips's Avatar
 
Join Date: Mar 2008
Location: Location, Location
Posts: 1,302
Rewards Points: 500
Default

26' Steel I Beam


that's fine, I'm not trying to pick a fight or derail a thread. All I'm saying is maybe we wouldn't have as many drive-bys if the answers were more on point. Simply saying " your question has too many variables to be answered here" is (IMO) a much more acceptable answer, but it sounds like I'm in the minority here, so I will leave it at that.

Sorry to hijack your thread OP, good luck with your project.
__________________
Those who can, do...
Those who can't criticize on the internet
Mr Chips is offline   Reply With Quote
Old 01-11-2011, 07:27 PM   #13
DIY Hack
 
Mr Chips's Avatar
 
Join Date: Mar 2008
Location: Location, Location
Posts: 1,302
Rewards Points: 500
Default

26' Steel I Beam


Quote:
Originally Posted by Joe Carola View Post
I don't care what you say, no one here can answer what size beam this guy needs.
Sorry, I know I said i was resigning from this thread, but i just saw the above statement. For the record, I NEVER said that anyone here could answer this. The first responder ( I'm too tired to see who it was ) said something like " I can tell you the size, but that's only a small part of the overall project". I was criticising that response as it almost sounded like he (she) was saying "I know the answer, but won't tell you until you prove you've done your homework".

Ok, enough from me on this, my point has been made, the votes are all in, looks like i lost this one! thanks guys
__________________
Those who can, do...
Those who can't criticize on the internet
Mr Chips is offline   Reply With Quote
Old 01-11-2011, 07:31 PM   #14
Framing Contractor
 
Join Date: Apr 2006
Location: Caldwell, NJ
Posts: 1,758
Rewards Points: 1,000
Default

26' Steel I Beam


Quote:
Originally Posted by Mr Chips View Post
that's fine, I'm not trying to pick a fight or derail a thread. All I'm saying is maybe we wouldn't have as many drive-bys if the answers were more on point. Simply saying " your question has too many variables to be answered here" is (IMO) a much more acceptable answer, but it sounds like I'm in the minority here, so I will leave it at that.

Sorry to hijack your thread OP, good luck with your project.
As I have said before, these people come here doing major projects on their homes with no intentions of have plans, permits and inspections. They ask the obvious questions that tell you this. When they are questioned they don't like it and don't come back because they are trying to do something illegal and dangerous.

Do you not care about people doing the right thing here by asking about drawings, permits and inspections? Or, all you care about is just answering questions and drawings, permits and inspections are not important for DIY'ers?

Would you ask how big a 26' beam should be on the internet and use someone's answers to let you know if you will do the job or not, or user that size as a reference? Can you answer these questions or will you avoid them like the people who avoid the plans, permit and inspection questions?
__________________
Joe Carola
Joe Carola is offline   Reply With Quote
Old 01-11-2011, 08:21 PM   #15
Experienced
 
Jackofall1's Avatar
 
Join Date: Dec 2010
Location: Southern Michigan
Posts: 2,822
Rewards Points: 2,000
Default

26' Steel I Beam


Quote:
Originally Posted by Mr Chips View Post
Sorry, I know I said i was resigning from this thread, but i just saw the above statement. For the record, I NEVER said that anyone here could answer this. The first responder ( I'm too tired to see who it was ) said something like " I can tell you the size, but that's only a small part of the overall project". I was criticising that response as it almost sounded like he (she) was saying "I know the answer, but won't tell you until you prove you've done your homework".

Ok, enough from me on this, my point has been made, the votes are all in, looks like i lost this one! thanks guys
I would answer the question as soon as mine are answered, in order calculate the beam size I would need to know the spacing, how many beams, just one on the outside wall with the inside wall sitting on an existing structure, or (2) center and outside, (3) inside, outside and center.

I trying to start a investigative conversation, I was and am more that willing to spend the hour or more to crunch some numbers in a spread sheet to given some estimates.

I was heading out in the snow storm to pick my wife up and was hoping on my return the answers would be there, instead you have mucked up the whole idea of why I was asking such questions.

Advertisement

__________________
When its all said and done there is usually more said than done
Jackofall1 is offline   Reply With Quote
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Question about steel I BEAM in basement djohns10 Building & Construction 7 06-23-2012 04:55 PM
How to repair main support beam Jerry48ece Building & Construction 0 01-08-2011 09:38 PM