Wring For Lincoln Power Mig Welder - Electrical - Page 2 - DIY Chatroom Home Improvement Forum
Old 01-14-2009, 11:28 AM   #16
DIYer
Originally Posted by Bondo View Post
Ayuh,... I've got that Welder,...
I've been running it plugged into a standard wall socket for Years now,.... No Problems....
They probably bank on the fact that a 20 amp circuit breaker will never trip with a 25 amp load that is as intermittent as a welder. Would likely take hours of continuous 25 amp load to trip a 20 amp breaker.
Gigs is offline   Reply With Quote
Old 01-15-2009, 11:05 AM   #17
Gentlemen, thank you all very much for your assistance and insight. It was all very good information. I found the answer to requiring a 20 amp circuit breaker while also requiring 25 amps available to that circuit in order to obtain the full output of the welder. As others have suggested, it's in the circuit breaker design and test criteria. The following is an excerpt from a circuit breaker manufacturer that explains the current carrying capabilities of most circuit breaker:
The CSA test program as well as our inhouse test program confirms compliance with the regulatory requirements by conducting the following tests:
Initial Trip time confirmation
  • The breaker is "over loaded" to a value of 135% of the current rating and the breaker must trip within one hour.
  • The breaker is then "overloaded to a value of 200% of the current rating and the breaker must trip in typically in less than two minuets.
Temperature test
  • The circuit breaker is overloaded to a current value of 6 times the rating ( but not less than 150 amp.) and switched 50 times.
  • The circuit breaker is then placed in a 40 deg. C. ambient temperature and forced to carry 100% of the current rating until the circuit breaker reaches thermal equilibrium. Temperatures are recorded and must be below the maximum temp. limits of the requirements.
Considering the welder's duty cycle it will operate at the 140 amps advertised by Lincoln so my previous assumptions were wrong.
vstoyko is offline   Reply With Quote
Old 01-15-2009, 06:15 PM   #18
Rewards Points: 270
Is this why my wife's 1875 watt blow dryer does not trip 15 amp circuit ? On the short list to change that to a dedicated 20 amp line...
pcampbell is offline   Reply With Quote
How do I get power to a new ceiling fan? sestivers Electrical 15 10-10-2016 04:16 PM
hooking up dryer....bronx ny code SURFBUG Appliances 6 10-14-2008 09:41 PM
Miller syncrowave 250dx Welder installation saddletramp Electrical 6 01-10-2008 01:11 AM
Problem W/ Power after Switching Outlets... G19-Fanatic Electrical 17 08-28-2006 01:55 PM
Partial power on same fuse! joyjam Electrical 5 07-10-2005 10:23 PM