#1 |
Workshop sub-panel in barn
Greetings,
I am looking to wire a sub-panel in my barn to support a general workshop. Loads would include standard woodworking tools (including 220V table saw), welding, air compressor, etc. The house has 200AMP main breaker and minimal in-house loads. Dryer is gas, Oven and cooktop are gas. Water heater is off the oil furnace. I think the biggest single load is the well-pump and/or fridge compressor. We do have sporadic toaster oven, hairdryers etc. Otherwise its just lights, ceiling fans, flat-panel tv, stereo... We had 4" conduit installed to the barn, so there is plenty of room to pull a big cable. The entire run from the house panel to the barn totals around 155' (probably less, but rounding up) My questions are:
Thanks for any thoughts you can share on this! Cheers, pete |
#2 |
it all depends on the actual equipment loads but with a 200A service and mostly gas appliances, 100A should be no problem. you have a 4" conduit running out there which is going to be big enough to handle anything you want out there.
4/0 aluminum USE is good for 180A at 75 degree C terminations (i presume you have 75 degree c circuit breakers) so you could put a 150A or 175A panel out there if you wanted to. if you only want 100A, #1 aluminum just makes it. what type of conduit is it? i'm guessing PVC. no problem at all getting the 4/0 in there. |
#3 |
Thanks for the thoughts itsnotrequired. 4" PVC conduit is right. I'd like the possibility of "upgrading" later, so maybe the 4/0 aluminum is good as it gives me a bit of stretch room if I want.
Do you have any thoughts on the additional sub-panel in the garage? Would I think of that as a sub-panel on the garage and then a sub-sub-panel off of that in the barn? Or is it just better to run 2 separate runs - one for the garage and one for the barn? Thanks! |
#4 |
not sure of the exact layout of the house, garage and barn but it is permissible to have 'sub-sub' panels. just need to consider that the first sub needs to be sized large enough to carry both subs and that depending on the breakers, you may have coordination issues where a problem on the sub-sub causes the sub breaker to trip but that would be pretty unusual. if it were me, i would run them separate from the main panel.
#5 |
Thanks for the info, itsnotreq'd. The layout is such that the garage is literally right on the way to the barn. I'm leaning toward separate runs anyway - just to keep things clean-o.
#6 |
Licensed electrician
You can have sub subpanels, but you can only have one feeder to the building. You cannot have a feeder to each subpanel in the building from another building.
Answers based on the National Electrical Code. Local amendments may apply. Check with your local building officials. |
#7 |
Thanks, Jim. The garage is in the house so in either configuration the barn will have only one feeder.
| Display Modes | |
| Garage Sub Panel Questions | mscanlon01 | Electrical | 3 | 07-20-2011 11:03 AM |
| Wiring a sub panel to another sub panel | Uncle Wayne | Electrical | 25 | 02-08-2011 10:50 AM |
| Subpanel next to Main panel wired the same in 1990 | Uncle Wayne | Electrical | 3 | 01-20-2011 01:43 AM |
| Passing wire to another panel | theatretch85 | Electrical | 5 | 09-21-2009 12:09 AM |
| Moving several circuits to sub panel | WoodworkerDave | Electrical | 2 | 09-27-2008 03:05 PM |