Workshop Sub Panel - Electrical - DIY Chatroom Home Improvement Forum
Old 06-30-2013, 09:37 PM   #1
Rewards Points: 81
Workshop sub panel
Finishing up my 1500sq ft workshop and I want to run my electrical service soon. I have a decent amount of experience with this but want to run my plan by you guys to see if you see any problems. First,my shop is 150ft from my 200 amp main panel located in the basement of my house. My main panel is a square d homeline panel. I plan to install a 125 amp breaker in my main panel which I sourced online. I will run THHN #1 (4conductors) through 2" conduit. In my workshop I am going to install a 200amp homeline panel mainly due to available circuits. Neutral and ground unbounded. Ground rods at shop needed? Also, can my ground wire be smaller?
hartkem is offline   Reply With Quote
Old 06-30-2013, 09:48 PM   #2
Electrical Contractor
jbfan's Avatar
Rewards Points: 478
Check the specs of the panel before you order the 125 amp breaker.
Most panels on allow a 100 amp branch breaker.
Other than that, your plan is fine.
Old 06-30-2013, 10:04 PM   #3
Rewards Points: 81
How can I look up the specs? Numbers on the box somewhere then look up online?
Old 06-30-2013, 11:17 PM   #4
" Euro " electrician
frenchelectrican's Avatar
Hartkem.,
You should have model number in the front of the cover door or it will be located inside the panel useally either right or left side of panel but becarefull when you try to find the numbers make sure you watch out the conductors.
If this is SqD or GE or ClutterHammer or Seamens or other ??
Most will take 100 amp two pole breaker without issue but some may take larger like 125 amp two pole breakers.
If you still not sure just take a photo of whole panel one of us can indentify so we can guide ya in correct way.
Merci,
Marc
The Following User Says Thank You to frenchelectrican For This Useful Post:
MTN REMODEL LLC (06-30-2013)
Old 07-01-2013, 08:17 PM   #5
Rewards Points: 81
I checked my panel tonight. It is a square D HOMC40UC. Can this panel support 125 amp breakers?
I also got a final measurement on the length of service wire I'm going to need. It's more than I originally thought at 210ft needed with a little extra factored in to be sure. I think I might have to switch to aluminum 1/0 to keep this affordable. I'm not familiar with aluminum wire. Is it single wire like THHN or is it in a bundle of four conductors. If you reply with acronyms please spell them out so I can understand thanks!
Old 07-01-2013, 08:35 PM   #6
Licensed Electrician
k_buz's Avatar
Rewards Points: 2,006
I wouldn't concern yourself too much with voltage drop. It's not like you are going to be drawing 100A.
Old 07-01-2013, 08:43 PM   #7
k_buz's Avatar
I can almost guarantee that you will be limited to 100A per stab. So, you will not be able to have breakers directly opposite your 2P 100A breaker. That being said, you would only need #3 CU or #1 AL for 100A...#2 CU or 1/0 AL for voltage drop.
The Following User Says Thank You to k_buz For This Useful Post:
MTN REMODEL LLC (07-01-2013)
Old 07-02-2013, 05:15 PM   #8
Rewards Points: 81
After talking to my electric company I found out they will provide a double tap meter socket so I can avoid hooking to my main panel using a breaker. Now that in not limited by the breaker size I'm going to run 4/0 aluminum for 200 amp service. Do I still need 4 conductors
Old 07-02-2013, 05:21 PM   #9
Good plan and a great savings
Handyncheap is offline   Reply With Quote
Old 07-02-2013, 05:31 PM   #10
k_buz's Avatar
You are opening a big can of worms. Service disconnects need to be grouped. Adding a line from the meter will mean that one disconnect will be in your current panel, and one will be in your workshop...not grouped. Depending on where your main panel is located you will need at least one more disconnect.
Now, here is the area I'm not 100% sure of. You have an existing 200A panel, and are adding a 200A panel, you are most likely going to be required to protect the conductors on the line side of the meter at 200A. If you don't you could be pulling more current than what your wires are rated for.
The way I'm envisioning this going down, you aren't even going to need the 2 lug meter socket.
You are going to need to pull a permit on this, and as such, you should really talk to your inspection department to see if what you want to do is legal.
Old 07-02-2013, 09:50 PM   #11
Rewards Points: 81
K,buz
I live in the county and there are no inspections. The only jurisdiction is the electric company. They put me in touch with the engineer in charge of my particular area and I asked him about the double lug meter socket. He advised me that all I needed to do was remove the old meter socket. Install new double lug meter socket and reconnect service to the hose which is located in the basement directly beneath the meter socket mounted on the outside of my house. I would then need to run the extra lugs to a 200 amp disconnect before going underground to my shop. Is this not Ok.
Old 07-02-2013, 09:57 PM   #12
Rewards Points: 81
I forgot to add that he said the service wires from the transformer which are buried are 4/0 al and they only have 200 amp meter sockets. So the new double lug meter socket would also only be 200 amps. He specifically said both buildings would be essentially sharing the 200 amps. My question is what happens if in the unlikely event the house and the shop both draw 150 amps for a total of 300. What protects the 4/0 wire between the transformer and meter?
The Following User Says Thank You to hartkem For This Useful Post:
MTN REMODEL LLC (07-02-2013)
Old 07-02-2013, 10:07 PM   #13
Licensed electrician
Rewards Points: 1,612
Your power company may allow this, but it does not meet the National Electrical Code for the reasons KBuz posted above.
Old 07-02-2013, 10:39 PM   #14
Rewards Points: 81
Wouldn't NEC 230.40 exception 2 allow this since my buildings are not attached
Old 07-02-2013, 10:50 PM   #15
Resi EC
Rewards Points: 252
Don't have my 2011 NEC (in truck) but the 2008, 230.40 exception 3 should work. IF I read it correctly.
A single-family dwelling unit and a separate structure shall be permitted to have one set of service entrance conductors run to each from a single service drop or lateral.
That may have changed in the 2011 NEC, so it may depend on which code cycle you area is under
If at first you don't succeed .... do not work on live electrical
Gac66610 is offline   Reply With Quote
Multiple Panel Question theatretch85 Electrical 7 09-29-2016 07:15 PM
Main Service Panel to 2 breaker panels - I can imagine you all rolling your eyes kalus Electrical 22 03-23-2012 02:09 AM
Mobile Home Electrical Panel Replacement rrolleston Electrical 2 01-28-2012 05:27 PM
200A upgrade and move, backfeeding permitted? WillK Electrical 3 05-30-2011 08:00 PM
turn main panel into a sub panel? tikicarver Electrical 2 01-24-2008 07:37 AM