-   -   Wood shop 100 amp sub panel (http://www.diychatroom.com/f18/wood-shop-100-amp-sub-panel-171390/)
tinybear 02-08-2013 02:36 PM
DIY members, just wanting to run this by you guys on my plans to upgrade the panel in my wood shop. The situation is my main panel is attached to a pedestal along side my meter. ( I live in a mobile home ) Right now the wood shop (a detached building) is fed with a double pole 40 amp breaker [ #8 AWG NM-B copper inside 1 1/4" conduit, [ I know its not code, but we're gonna change that ] about 50' in length] I installed coming from the 200 amp service that also powers my mobile home. The panel in my mobile home is a 100 amps. My plan is to install another 100 amp sub panel [ powered with #2 AWG THHN copper with neutral and equipment ground, from lugs at the base of the buss bars in the 200 amp main panel ] to replace the existing small panel in the wood shop I am using now. What I want to do is use the same small panel and move it to the other end of the shop using the same 40 amp breaker with the #8 feeder that exist now and be ready for the future shop expansion I'm planning for the spring. It will be used for a lighting circuits and dedicated GFI protected wall and exterior recepticles. One of the questions I have, will I have to install two more grounding rods where the second sub panel is going ? Also, I want to use some EMT conduit ( 1/2" w/ 4 #12 THHN wires ) to surface mount a couple of 220v receptacles. The interior walls of my shop are sheathed with 1/2" CDX. What is the proper way to exit the wall bay ? [LB inside wall bay, short length of EMT to another LB on the outside ? ] I know this is a long winded request, but I wanted to try and get all the info you guys might need to help me out ! Thanks
rrolleston 02-08-2013 02:42 PM
You can't go off the lugs with #2 wire. You will have to use the proper sized breaker in the panel to go to your shop.
oleguy74 02-08-2013 06:14 PM
useing feed through lugs,you have to size your wire to the required size for the 200 amp main breaker.3/0 copper or 250 aluminum.
rrolleston 02-08-2013 06:45 PM
Why 250 al
tinybear 02-08-2013 06:47 PM
In my original post I failed to state the proper size feeder to my sub panel. Actually it's 2/0 AWG THHN, and now I realize its still too small. I'll use a 100 amp breaker at the main to feed the sub, also with a 100 amp main breaker. Thanks oleguy74. Would sure like to meet rrolleston with his special discount and that "cocky attitude" of his ! Sounds like he needs a little tune-up. People from Grandville, what do you expect ?
rrolleston 02-08-2013 07:03 PM
3 2/0 and one #6 ground in a 1-1/4 is way too much.
Stubbie 02-08-2013 10:31 PM
Not exactly this only applies if your feeding a main lug panel from those lugs and both panels are indoors..
Since his service equipment is located outdoors on a pedestal he is allowed to use his feed thru lugs to feed a 'main breaker' panel so long as that main breaker is sized properly to protect the conductors of his feeder. Lookup unlimited tap rule in the NEC. It's not a lot different than what is going on from his service equipment to the main breaker panel in his house. I belive you can also use the summation rule for the sub if a main breaker does not exist.