Wiring For Two Kitchen Gfci Outlets... - Electrical - DIY Chatroom Home Improvement Forum
Old 12-27-2010, 08:22 PM   #1
Wiring for two kitchen gfci outlets...
Hi all,
I am in the midst of a kitchen reno and want to replace an existing receptacle that is wired with 12/3 aluminum and fed from a double 15a breaker (with tied handles).
I would like to change this to a pair of gfci receptacles (one on either side of a sink). My question is what wires should I run and can somebody point me to a wiring diagram? I am confused by some posts I've read and believe I need 12/3 copper from the panel to the first receptacle and 12/2 copper from the first receptacle to the second?
Cleon26 is offline   Reply With Quote
Old 12-27-2010, 08:27 PM   #2
Electrical Contractor
jbfan's Avatar
Rewards Points: 252
Are you in Canada?
Are you running new wires?
Old 12-27-2010, 08:41 PM   #3
Yes in Ontario and running new wires...
Old 12-27-2010, 09:56 PM   #4
Running 12/3 aluminum from ganged 15 amp breakers was code acceptable in Ontario during the 70's.
Presently, the code requires that a receptacle within 5 feet of a sink is to be GFCI protected.
You can use ganged GFCI breakers, however these are expensive.
The code now allows 2-20 amp receptacles to be installed if they are closer than 5 feet to the sink.
They are fed from a single pole, 20 amp breaker, on 12/2 (copper)Romex that terminates on the LINE terminals of a 20 amp GFCI.
The second receptacle is a standard 20 amp one, that is fed by 12/2(copper) that is fed from the LOAD terminals of the GFCI.
Old wiring in kitchen donnek Electrical 8 11-16-2010 02:47 PM
question about wiring outlets? bfan781 Electrical 1 10-28-2010 09:25 AM
Kitchen GFCI with 12/3 feed zapped Electrical 17 10-23-2010 11:15 AM
Funky wiring in Kitchen Atreyou40 Electrical 10 08-24-2009 11:05 AM
why would kitchen outlets stay on if 1 leg out pag Electrical 4 05-05-2009 07:45 PM