Ok. I understand. This is a low environmental impact project. So I think it will all work with everyone being conscious of energy usage. I am glad to know that a 10% voltage loss is acceptable. I guess a number 2 or 3 wire will do the job.
At 700 feet the kitchen will be built. Then 700 feet further along the cabins will be built. Most of the power will be used at the kitchen. Could I use a smaller wire from the kitchen onwards to the cabins if I set the cabins up as a sub circuit?
SWAMI is offline   Reply With Quote
Old 07-21-2008, 06:07 AM   #17
nap
You talking to me?
nap's Avatar
Rewards Points: 6,290
Sure. Here are a few links to voltage drop calculators. If you need help in figuring out how to use them, just ask.
http://www.southwire.com/voltagedropcalculator.jsp
http://www.csgnetwork.com/voltagedropcalc.html
http://www.jhlarson.com/ind_tables/v...c_voltdrop.htm
and a page that has all sorts of electrical calculators that may aid you.
http://www.electrician2.com/calculators/elcal.html
Old 07-22-2008, 04:48 PM   #18
Before you buy even one wirenut I'd post a schematic or wiring diagram, and parts list, using Photobucket or some such service, as complete as you can make it.
Schematics speak volumes and are unambiguous. Your calculations, including fault protection, would help, too.
Old 07-24-2008, 05:03 PM   #19
Now I am realizing that I need to buy Romex with the three wires (positive, negative and ground) wound together for direct burial, as opposed to THHN. Otherwise I would have to buy three separate wires for the entire run.
If I size the wire for the entire load of 2500 watts and run that 700' of the 1400' run, and then set up a sub panel on the same circuit from which to go the remaining 700' to the cabins where I will only use 1200 watts of the entire 2500, can use smaller gauge wire for the run to the cabins? According to the calculator, at a 10% voltage drop I could run #1 the first 700' to the kitchen and then use a number 3 for the rest of the run.
I don't quite understand the logic of the above proposal, but does it make sense to the more learned out there, the better wired?
Old 07-24-2008, 05:57 PM   #20
Recommendation
"A top-down approach is essentially breaking down a system to gain insight into its compositional sub-systems.
In a top-down approach an overview of the system is first formulated, specifying but not detailing any first-level subsystems.
Each subsystem is then refined in yet greater detail, sometimes in many additional subsystem levels, until the entire specification is reduced to base elements.
A top-down model is often specified with the assistance of "black boxes" that make it easier to manipulate. However, black boxes may fail to elucidate elementary mechanisms or be detailed enough to realistically validate the model."
So, your black boxes would be each of the wire segments, each transformer, fault protection, and any other "systems" necessary.
I know the temptation is strong to already start buying parts.
One constraint: the transformers may not be stable when feeding the long lengths of wire in the configuration you want. You should ask the manu; they may have application notes that exactly address your plan.
Once you're down to the detailed schematic and parts list, you'll think of more system level stuff, and so on, back and forth.
Old 07-24-2008, 07:35 PM   #21
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,956
HUH???
Does ANYONE understand this gibberish?
Yozit, not everyone understands, nor wants to understand, your engineer mumbo jumbo. Why not try to talk (write) like a real person once in a while.
Old 07-24-2008, 07:43 PM   #22
Originally Posted by Speedy Petey View Post
HUH???
I don't. I am just trying to take a wire 1400' in a rain forest and turn some lights on on the other end, not fly to the moon. Heck, I can use a hand blender in the kitchen. Just lights will be fine.
Old 07-25-2008, 07:54 AM   #23
The writing problem and the power transmisssion problem is being worked.
Old 07-25-2008, 11:08 AM   #24
Mr. Swami, I've cut and pasted all your posts into a single document, and I have some questions on your statements before I put any more work into this.
Here is one scenario, the topmost level of this system design. Correct me if I'm wrong in the statements below and adjust the scenario to suit. Neglect losses for now. If there is anything below that you don't understand, ask.
Your turbine generates 500w continuously and you need 2500w in the buildings.
This means that 100% x 500/2500 = 20% of the time in the buildings you can consume 2500w.
The other 80% of the time the 500w turbine is charging the batteries and you have no power in the buildings.
If the general requirements above are not met, this system is not feasible. The specific numbers can be tweaked but the basic calculations must be adhered to.
Knowing only what is written above, one conclusion you can already draw is that the battery/invertor should be right outside the buildings, since the heavy power is transmitted from the batteries to the buildings. The really long wires should be carrying the charging power since it's only 20% of the total power that we are sending over this network.
Plugging in some numbers, 20% of 24 hrs is ~5 hrs for the discharge time and ~19 hrs is the charge time.
The battery needs to supply 2500w for 5 hrs which gives a battery capacity of 12,500 watt hours. At 48v, this is 260 amp-hours.
Questions:
What is the capacity of your batteries?
What is the recommended charge/discharge rates for your battery?
During the 19 hrs, what minimum power can you live with, if not zero? 100w to power a bulb?
Is there some other charge/discharge cycle besides 24 hrs that we could/should use? The battery manufacturer's recommendations will determine the minimum charge/discharge cycle and how deep the discharge is, for reasonable battery life.
If this is all still feasible, I need to find a way to post a spreadsheet.
Old 07-25-2008, 12:43 PM   #25
Mr.
Questions:
Here is the battery info. Deep cycle 6 volt L 16H. Six of them. With DOC at 20% they will last for 6 years
http://www.plymouthbatterycentre.co....cycle_battery/
The light bulbs are only 20 watt compact florecents.
Need the fridge going full time at 110 watts, but it actually goes off and on itself as need be. So it actually does not use 110 watts all the time.
Lights will be used for a maximum of three hours in the morning and three at night. Although each cabin has two lights in the main room, one in the bathroom, and one outside most of the time it will be the two inside lights on.
Thanks!
Old 07-25-2008, 01:14 PM   #26
Thanks!
Thanks. I have to think about this some more.
But, it turns out there is a level of design more abstract than the one I wrote. It's this:
A system of turbine, cable, battery, invertor delivers power.
The turbine delivers 500w averaged over 24hrs.
A battery can be charged for 16 hours and you only get 10 hours of service, so the battery efficiency is 100% x 10/16 = ~63%, which means 100-63 = 37% is lost.
Let's say all the other components total 10% loss.
Total loss ~ 50%
This leaves you with 250w averaged over 24 hrs at the building.
Is this still feasible?
If not, you need more turbines or you need to intercept the 60w per square foot that sunlight provides. At 10% efficiency, a photovoltaic array delivering 2500w needs ~420 square feet, about 20' on a side.
Windpower I can't comment on, but in Massachusetts they use a 100' boom to mount the blades, generator, gearing, disk brake and whatnot.
Old 07-25-2008, 01:39 PM   #27
Total loss ~ 50%
I think so, but during the rainy season I could generate twice the power from the turbine. Whereas at the end of the dry season I will need solar panels to augment the system. These same panels could then increase the potential power that much more during the rainy season.
Much more helpful. Thanks!
Old 07-25-2008, 04:18 PM   #28
The batteries are the weak link so you might look into Flywheel Energy Storage. Don't know the cost of these state-of-the-art things but over a long time they might pay for themselves.
I can't write nearly as well as I thought I could. . .glad I could finally help.
Old 07-26-2008, 09:43 AM   #29
Please excuse the type font and size ; I'm still having computer problems.
Component Specifications
So the battery is 36v nominal volts at 420 a-h capacity, right?
I need links to get specs on your invertor and turbine/gen arrangement.
Loads
What is each load,
how often is it used,
how many of them are there?
I'm trying to get an idea of the steady state load, the total energy used over 24 hours, and any peak loads (compressors, motors).
I will assume that the fridge pulls, on startup, 5x the normal (steady-state) current, and that it's on half the time. The fridge people might be able to tell you the expected duty cycle of the fridge based on the ambient room temp, but I'm not sure we have to worry about that yet, or at all.
Cabling
Copper wire at 100C has 1.3x the resistance at 20C because of the temperature coefficient of resistance of copper.
Cabling temp rise will be due to ambient temp plus the heating effect of carrying current.
So, what is the highest amb temp you reasonably expect to see? Ampacity and the particular wire insulation is another issue, TBD.
You mentioned a 10% voltage drop on cables; depending on the circuit, if we go to a 5% drop we can cut the cable loss to 1/2 of what it is at the 10% drop, but the wire will cost more. And it may not matter much because of the battery inefficiency swamping out all other losses.
Configuration
Based on my reasoning in a previous post, do you now want to put the invertor at the end of the 2400' cable from the turbine, or is this non-negotiable?
In fact, in general please indicate "design goals" and "minimum values" you can live with. Any extra power during the rainy season is fine.
You've got one kitchen, 6 cabins, cable lengths of 1000', 1400', 700' and 500'.
Please post a scale drawing of how this looks from above.
I think you want the cabin wiring to radiate out from the kitchen in a star configuration (rather than daisy chaining each cabin downstream of the one before).
Post photos of everything; electricians can pick up safety issues that I would not see.
Economics
Since you're not paying for kwh, and aside from not designing a system that abuses the daylights out of the generator, batteries and invertor, are there any economic payback issues that we should consider?
Misc
I assume you have access to a spreadsheet?
There is another way to store power. You pump water uphill to a holding pond and then let the water down through a turbine during periods of peak demand. I don't know the efficiency of this method, and it may only pay off for huge installations.
Old 07-26-2008, 10:52 AM   #30
[QUOTE=Yoyizit;143193]]I need links to get specs on your invertor and turbine/gen arrangement.[/SIZE]
Here is the turbine. It's the Stream Engine with two nozzles.
http://www.microhydropower.com/
Here is the info on the inverter, It's the 3600W VFX 3648 48V
http://store.altenergystore.com/Inve...Inverter/p929/
I think we could also discharge the batteries down to 50% and still get plenty of life out of them. Actually it's a 48V system. So 8 6V batteries
I will get you more info later. We are beginning a two day retreat today that will end Sunday evening. So I will get back to this after that.
I really appreciate the help.
Wiring diagram for three-way switches with pilot light SaxTeacher Electrical 34 09-15-2013 07:53 AM
Size of whole house fan needed Doug Crf General DIY Discussions 20 02-25-2011 11:29 PM
2x100a sub on service main jambud Electrical 17 03-12-2008 09:31 AM
Replacing wiring in middle of run, ungrounded lighting circuit alexz Electrical 3 07-05-2007 08:53 PM
Knob & Tube wiring - How concerned should we be? hotdiggitydog Electrical 6 04-11-2006 07:52 PM