-   -   Wiring a shed, need advice. (http://www.diychatroom.com/f18/wiring-shed-need-advice-132252/)
hgbpro 02-01-2012 06:50 PM
I want to get power to my 12 x 20 utility shed. I would like to have 2 circuits. One for lighting only. And one for recepticals. Here is what the power will be used for.
Lighting circuit:
1 - exterior flood light (dual head)
3 - interior 60watt bulbs
Receptical circuit:
1 - outlet to plug in a full sized refrigerator that will run 24/7
1 - 4way outlet box that will operate tools such as, chop saw, skill saw, drill charger, phone charger, etc..., nothing big.
Maybe I only need one circuit for this? Rather have overkill than not enough? You tell me...
My run from the house to the shed is 30ft max, including up into the breaker on the house.
My main questions are:
1) what type/size wire do i need to feed from the house to the shed.
2) what size and how many breakers do i need to add to my house panel?
3) can i bury the wire direct in the dirt, or does it have to be buried in conduit?
4) what type of breaker box do i need in the shed, if any?
5) Do i need to run two seperate circuits from the house, or can i run one feeder and split it at a panel in the shed?
Thanks to anyone who helps me. i need specifics on all items I will need to buy. i have no clue what THHN,UF, or AWG mean. I have alot of low voltage experience but this is my first diy for high voltage. Thanks
a_lost_shadow 02-01-2012 07:39 PM
1,2, &4) Depends on whether you have a sub panel at the shed. I don't recall the requirements, so I'll leave this to others. However, I would recommend totalling up the wattage of everything that you want. That will give you an idea of how many circuits you need. Depending on the wattage, you might want to do fridge + lights on the first circuit, and everything else on the second.
3) Depends on the type of wire. Some wire can be directly buried, others require conduit. Additionally, the depth it needs to be placed depends on if there's conduit and what type. How much do you want to dig? Also if you lay conduit, it makes it much easier if you ever need to replace the line in the future.
5) You can always put a sub panel outside the shed, and branch off there. Again I'm not sure if you can run multiple circuits from the house to the shed without a sub panel out there. Am I correct that the shed is completely detached?
THHN - Single conductor wire for use in dry environments, must be in conduit
THWN -Single conductor wire for use in dry/damp/wet environments, must be in conduit
UF - Multi-conductor cable (like NM-B aka Romex) that can be buried directly and used outdoors. Needs to be protected if subject to damage (i.e. running down the side of a building)
AWG - American Wire Gauge (a unit for measuring the size of a wire. Smaller #s equal larger wires in the #NN ranges. At 0 it flips over and x/0 is larger for larger values of x)
If you don't know what wire gauge is, than I'm extremely concerned that you're out of your league. If you just hadn't heard the acronym AWG, then you've just got a bunch of reading to do. I suggest picking up a few DIY books on electrical wiring. While subpanel wiring is within the DIY realm, it shouldn't be your first introduction to working with 120/240V.
There are other questions that will need to be answered:
- How far is the shed from the house?
- Do you have to go through the house to get to the shed, or is the meter on the same side of the house as the shed?
hgbpro 02-01-2012 07:55 PM
shadow,
thanks for the reply. I do have knowledge of wire gauges. Just had never heard the acronym AWG. thank you for the low down on all the acronyms. The shed sits 25 feet from the house and is completely detached. theindoor home breaker panel is on the same side of the house as the shed, directly across 25ft. the houses outside panel is on the far side of the house from the shed. it is more convienent for me to use my indoor panel on the house as my source. After your suggestion, i will use conduit. Will the grey PVC type suffice? I will be dropping down from my breaker panel into my crawl space and then through the wall of the crawl space to the exterior of the house, then I will run the conduit down the rest of the foundation into the ground and across the yard to the shed. Is 18" deep enough if using the conduit? Thanks for the help
TarheelTerp 02-01-2012 08:59 PM
Cutting to the chase...
it's just as much bother (and expense) to pull one set of larger wires vs 2or more sets of smaller.
So? Pull bigger wire. I'll suggest using 6/3UF cable or wire in PVC conduit (have to trench either way).
And yeah, set a small sub panel box out there.
Have (almost) as many circuits as you like.
zappa 02-01-2012 10:44 PM
Originally Posted by hgbpro (Post 841675)
Will the grey PVC type suffice? Yes, it needs to be rated for electrical which the grey normally is.
Is 18" deep enough if using the conduit? It depends on your area and frost depth. I would check with your local codes and see what they suggest.
Stubbie 02-02-2012 12:08 AM
1 Attachment(s)
Table 300.5 NEC
PlumbDumb 02-02-2012 12:32 AM
Well said Tarheel.
Pulling 6/3 through condo into a nice 50amp sub panel will give you everything you could need. Id like to offer some advice, as a plumber by trade i just completed a similar project for my uncle. So i have been binging on electrical books, forums, and distracting electricians on the job with hand drawn diagrams to make sure I didn't become "that guy".
If you run 6/3 through conduit, your 50amp sub panel will have: 120v, 240v, (the extra conductor brings a second phase of 120v to the panel, which a double pole breaker can send both phases to a future 240v appliance like an air compressor/welder/heater), neutral and ground protection. This also distributes the load of your entire shed over the 2 120v phases, and not a single leg.
Refrigerators should really be on their own dedicated 20 amp breaker wired in 12/2.
Your lighting load is not too bad, so keep all your lights on one 15amp breaker. This way you eliminate switches, boxes, and junctions: when you want light, just flip the breaker. You can even run 14/2 for your lights (at least in my area) but sometimes its easier to just use 12/2 for everything. If you use 14/2, you must only use a 15amp breaker. 15a breaker protects 14 gauge, 20a protects 12.
Chop saws/120v air compressors and a bunch of other common tools run at the higher end of a 20a breaker, especially when they first start up. I say pimp your quad box: Put each of the 2 outlets on their own 20a breakers. This will give you a huge advantage: Chop saw on one breaker, air compressor on the other, then use the remaining 2 sockets to plug in your chargers/low current stuff and you can get every last bit of 40amps out of one quad box, as opposed to 20 amps across all 4 sockets on one breaker. Installing 2 GFCI outlets could save your life one day.
20amp-fridge-12/2 15amp-lighting-14/2 20amp-1st outlet-12/2 20amp-2nd outlet-12/2
Stupid plumber, that's 75amps of breakers! Chances are 3 of your heaviest tools and the fridge will not all fire up at the same time as you hit the lights. All of your stuff should play nice on the 50amp, double pole breaker protecting your 6/3 feed. If you wanted to really knock it out of the park, make it a 100amp sub panel: just pull 4/3 and connect it to the main panel with a 100amp breaker. Just make sure the panel is rated for whichever amperage you pick.
As of right now you need 4 breakers for 4 circuits in your shed. So grab a 50amp sub panel with space for at least 6 breakers: the 4 now and at least one future 240v or 2 future 120v circuits.
Julius793 02-02-2012 12:35 AM
Remember there must be a main disconnect at the shed
Julius793 02-02-2012 12:41 AM
Originally Posted by PlumbDumb
Well said Tarheel.
If you run 6/4 through conduit, your 50amp sub panel will have: 120v, 240v, (the extra conductor brings a second phase of 120v to the panel, which a double pole breaker can send both phases to a future 240v appliance like an air compressor/welder/heater), neutral and ground protection. This also distributes the load of your entire shed over the 2 120v phases, and not a single leg.
Refrigerators should really be on their own dedicated 20 amp breaker wired in 12/3. A fridge on a 15amp will probably over-draw the breaker at startup, but the load lessens quick enough to keep it from tripping. Longer breaker life with a 20amp.
20amp-fridge-12/3 15amp-lighting-14/3 20amp-1st outlet-12/3 20amp-2nd outlet-12/3
Firstly a typical fridge doesn't need a 20 and will not trip on start up if it's a 15. Second when you say 12-3 that means 2 hots one neutral and ground. 12-2 is on hot one neutral and ground. My point being ground is not counted In the name.
PlumbDumb 02-02-2012 12:59 AM
thanks got my nomenclature messed up
frenchelectrican 02-02-2012 01:17 AM
Plumbdumb.,
There is one item you will have to remember that with most modern code if you ever run MWBC ( Multi Wire Branch Circuit ) you will need two pole breaker or with handle tier ( I am not too crazy with this part but it is legit )
A Lost Shadow .,
In case you look for the THHN / THWN conductor they genrally are dual rated for both dry and wet location purpose.
Merci,
Marc
PlumbDumb 02-02-2012 01:52 AM
When i installed my sub panel i used an MLO sub panel protected by a double pole breaker at the main panel. Is that illegal?
Julius793 02-02-2012 03:53 AM
If it's in a separate structure than it must have a main disconnect.
zappa 02-02-2012 05:07 AM
Originally Posted by Julius793 (Post 841914)
If it's in a separate structure than it's not per code.
Huh? :blink:
Did he PM you with the number of breakers in his panel?
Julius793 02-02-2012 05:36 AM
Originally Posted by zappa
Huh? :blink:
Your right I redid my post.