#1 |
Wiring Problems
Okay I'm in neck deep in a wiring project that is getting worse by the moment. It started when a breaker popped after my son plugged in a stereo in his bedroom. In fact it more than popped, it died. I went to the HW store, bought a new breaker, and then about screamed when I took off the panel to the breaker box. Several hours and breaker flipping later, I ran into the following:
I'm sure there's more to come, but that's what I've found so far. This house is only 13 years old; I bought it 8 years ago and all hell is breaking loose just now. This is one of those "I wish I had known then what I know now" situations. Anyway, now for the questions:
I'd love to be able to afford to have an electrician come in and do it all for me, but unfortunately I lost my job a year ago and the disability just ran out. I'm trying to bring the house up to code so I can sell it and move into someplace more affordable. I used to do industrial wiring many many years ago, so I'm not flying blind here. |
#2 | |||||||
My License Ain't 4 Sale..
Wiring ProblemsQuote:
#3 |
Wiring Problems
Okay, more bad news. I pulled a switch in the bedroom and found the body was cracked across, and ungrounded. I replaced the switch. My next random choice was a panel of three switches in the living room. Opened it up, pulled out three switches and all three were cracked, and ungrounded. I just replaced those. My back is telling me to quit for the day, but I figured I'd update.
#4 |
Civil Engineer
Wiring Problems
You might as well replace all the wiring in your house. I had a similar problem when I moved in, the person who owned it before me was a "do it yourselfer" with limited knowledge, but boundless enthusiasm. He had done similar things, like splice various sized wires together to make a circuit, bury splices in walls, splice wire with tape (no wire nuts) without a box, install a 20A fuse on a 14 gauge wire circuit. I could go on, but you get the picture. So I replaced everything, new panels, replaced fused panels with breaker panels, new grounds.
By the way, it sounds like you do not have independent equipment grounds for at least some of your circuits. Since you are going to be replacing all the wiring in your house, you should make sure that each circuit has an independent equipment ground. As for your panel, as previously noted in one of the posts, it is required by NEC that the neutral and independent equipment grounds (IEG) be connected together at the first disconnect from the street ONLY. In other words, you DO NOT connect the neutral and the IEG together at a subpanel, rather you connect the neutral in the subpanel to the neutral bar in the main disconnect using an appropriately sized wire, and the IEG to the neutral bar in the main disconnect using an appropriately sized wire. |
#5 |
Wiring Problems
Update:
I installed a grounding bar on the second box, and I've rewired it as suggested. I should clarify, all circuits do have grounds. My comment above was that some of the light switches had ground screws, but the ground wire wasn't connected to them. Some of the other light switches don't have ground screws, but the ground wire is in the box with them. I took a look at the outlet on the front porch since it didn't seem to be working and found out that the post light at the end of the driveway is wired directly into it. In other words, I have to turn on the post light switch in order for the porch outlet to have power. In addition, the wiring to the post light was tied in to the line side of the GFCI, not the load. Finally, the wiring to the post light is basic NM cable that goes directly into the ground (no conduit). I had long suspected that was the case for the shed power, so I had disconnected it years ago (the shed was added on by the previous owner). I had thought the post light was original with the house, but now its not looking that way. I replaced five standard outlets in the kitchen with GFCI outlets. Other than the fact they should have been protected, the wiring looked fine. I went after two more switch plates and those weren't so fine. Two of four switches were cracked, one of which was so bad it literally fell apart in my hand into several pieces as I was pulling it out of the box. The last plate I went after was a two-switch, one GFCI outlet next to the sink. One switch was for the light over the sink and the other for the in-sink disposal. That's a happy little mess in there. Check out the picture. You should notice the WTH cable is a four wire: it has the common from #2, the switched hot from #2 for the disposal, and the hot from #6, plus ground. Whatever the hot from #6 is doing there I don't know, but I can't imagine its legit. Also, the grounds for both circuits are all tied together; I've not encountered this in household wiring before, but I'm guessing its not good (ground loops are a no-no for shielded cable). I see I'm pretty much going to have to go through every outlet and switch in the house and do this the hard way. This project appears to be going from "a simple fix" to "dismantle the house with a rusty spoon". I've never done drywall before, so the idea of rewiring the whole house is awful daunting. |
#6 | |
Licensed Electrical Cont.
The house is 13 years old. He does NOT have to re-wire the whole place. There are circuit grounds present, right in the image above your post. There would HAVE to be to pass any kind of codes in place in 1996. This was not that long ago. The codes for circuit grounds have barely changed, if at all since then. The requirement to ground switches is relatively new. My 1990 NEC has the old requirement that if the switch is mounted in an ungrounded box or a non-metallic box, and the switch is not grounded, then a non-conductive faceplate must be used. This was changed in either 1993 or 1996. 1999 has the requirement that switches must be grounded regardless of the type of faceplate used.
Sometimes I feel like if I answer any more questions it is like someone trying to climb over a fence to jump off a bridge and me giving them a boost. |
#7 | |
I moves into my 1975 house in 1993. I replaced every device in the house. Since then I have done it again using spec-grade receptacles. That's all I use now anyway. Replacing all of them is cheap insurance that the future buyer will have less to gripe about.
#8 |
It was a dark and stormy
Wiring Problems |
#9 |
electrician
Wiring Problems
Sunici, quit running around screaming your head off and talking about getting a lawyer. You have described nothing that is seriously wrong (except the splice outside of an enclosure) and that's nothing to get excited about, just put it in a box. All your ranting about 2 rooms sharing receptacles (allowed), whole basement on one circuit (allowed), gas stove not on a GFCI (allowed), 4 circuits for the lights in your house (allowed).
The biggest problem in your house is the subpanel that you installed and didn't separate the neutral and grounds. You would be much better off if you stop right now, take a chill pill, leave well enough alone, never touch anything electrical by yourself again, stop posting your silly little ideas on the WWW and find another hobby that won't wind up burning your house down. |
#10 |
Wiring Problems
Going by the pic of your switch box it doesnt look bad, it looks fine. Quick wire receptacles and switches with #12 wire broke many devices exactly like your pic shows. Pushing the device back into the box was a chore as the wire was stiff and people forced it in instead of easing it in.
Check your switches and replace as necessary, clean up the "dog turds"and make sure your current GFI's are protecting your kitchen recpetacles. |
#11 | |||
The wiring to the post light does NOT require GFI protection. Are you sure the cable is not UF cable. UF is/was not always grey, especially from that time period. Quote:
Also, how do you know they were not GFI protected? Just from the lack of GFI devices? You say there was a GFI near the sink. Again, a house from this period would definitely require GFI protection for some/all kitchen counter receptacle. The code requiring all counter service receptacle to be GFI protected was a change for the 1996 code cycle. So it is entirely possible that only receptacles within 6' of the sink were required to be protected and your house was perfectly complaint. Quote:
It is carrying a feed to something, possibly the DW. The red is switched, the black is not.
#12 | |
Who does he think he is going to sue...and for WHAT???? This is a sadly typical mindset.
#13 |
Wiring Problems
It's kinda hard to tell from the pics, but does it look to anyone else that the neutrals of the the #2 and #6 circuit and the neutral in the 3-wire are mixed up?
#14 |
Wiring Problems
Not to me. The feed out neutral for #6 is hidden at the cable but plainly visible at the splice along with the light SL neutral.
To me it looks like #2 feeds line side of the GFI and then out to another box. I see #6 feeding the disp and light switches with a feed out to another box as well via that 12/3.
#15 |
Wiring Problems
First off, I was joking about the lawyer business. I'm not a sue-happy person; I've never sued anyone for anything. I'm sorry if I hit a nerve. Second, I'd prefer if you kept your comments civil. If I'm getting wound up over nothing, by all means let me know, but please don't belittle me while doing it. My industrial wiring experience was about a year's worth back in the mid-80s. The company had a lot of rules that went above and beyond code, and I'd have gotten my head chewed off over a lot of stuff I'm seeing in the wiring in my home. Forgive me if I'm overreacting.
As for the non-GFCI outlets in the kitchen, they were not protected. The one circuit (#10 breaker) had three outlets, none of which were GFCI. They are more than 6' from the sink, but the fridge is on one of those outlets and it has a water line for the ice maker. I replaced two, and the third one is downstream from the second so it is protected now. I suppose I could have saved a few dollars and only did one of them. The second kitchen circuit (#14 breaker) had one GFCI plus two regular outlets. Tripping the GFCI outlet did not shut off the other two outlets, so I knew they weren't protected. I replaced one outlet and the second (the stove) is protected because its now on the load side of the one I replaced. The third kitchen circuit (#1 breaker) consists of one outlet on the north wall plus one outlet in the hallway. I suppose that side of the kitchen could be declared the dining room, but I replaced it with a GFCI anyway. I've got a freezer plugged into it, so its kitchen to me. The fourth circuit (#2 breaker) had two GFCIs plus the switched disposal outlet under the sink. The disposal outlet was not GFCI nor was it on the load side of the existing GFCI. This is the picture I included above. I'll clarify the WTH: the 4-wire cable goes to the outlet under the sink: red=switched #2, white=neutral #2, black=hot #6, bare=ground #2 & #6. The biggest objection I had with this setup was the #6 hot was paired with the #2 neutral. All four wires end up in the outlet box under the sink; red/white/bare connects to the outlet, and black/white/bare goes off into the wall to some location unknown. The other lights on #6 are upstream of this box. (The dishwasher is on breaker #4 all by itself.) I did recheck the cable to the post light and it is UF. My old company would have put it in conduit; I thought all buried wire was supposed to be that way. Moles, shovels, and all that. |
| Display Modes | |
| electric wiring in house remodel | wis_remod | Electrical | 6 | 04-02-2009 03:40 PM |
| Wiring diagram for three-way switches with pilot light | SaxTeacher | Electrical | 33 | 03-18-2009 08:11 PM |
| New Home Wiring - Seeking Expert Advice | Dirtrnr | Electrical | 3 | 02-10-2009 11:33 AM |
| Elec short causing A/C problems or A/C problems causing elec problems? | Marlon | Electrical | 2 | 06-25-2008 03:04 PM |
| Knob & Tube wiring - How concerned should we be? | hotdiggitydog | Electrical | 6 | 04-11-2006 08:52 PM |