-   -   Wiring Plan (http://www.diychatroom.com/f18/wiring-plan-146443/)
navid 06-08-2012 05:55 PM
Wiring Plan
I am finishing my basement and this is the wiring plan that I am going to present to Ontario electrical inspector. I would appreciate any suggestion regarding the wiring.
http://i46.tinypic.com/14wr5o4.jpg
To be considered:
1- According to local electrical code I can do the job.
2- According to Local building code , having a kitchen in the basement is not permitted.
3- All the lights except Bath wall-mount light, are recessed IC.
TarheelTerp 06-08-2012 06:33 PM
That's purty.
Does it work?
AandPDan 06-08-2012 07:30 PM
That's a lot of stuff on 3 circuits.
Are you allowed to put the bathroom and other rooms on the same circuit in Ontario?
I think there is a limit to how many outlets (meaning lights and receptacles) you can have on a circuit in Canada.
navid 06-08-2012 08:07 PM
Thanks for your reply.
Rule 26-710 [C] : Bathroom Plug Outlet might be supplied with any nearby lighting circuit which has 11 or fewer outlet.
The maximum outlet number (lights and receptacles) is limited to 12, but according to Rule 8-304 : Where the load is known the Code permits more than 12 outlets on a 15 amp circuit provided the total load current does not exceed 12 amps.
In this case, the marked maximum lamp size on the fixture is known and no other loads is connected to this circuit.
AandPDan 06-08-2012 08:34 PM
No offense but remember that when you're watching TV and someone plugs in a hair dryer and trips the breaker.
The maximum outlet number (lights and receptacles) is limited to 12, but according to Rule 8-304 : Where the load is known the Code permits more than 12 outlets on a 15 amp circuit provided the total load current does not exceed 12 amps.I n this case, the marked maximum lamp size on the fixture is known and no other loads is connected to this circuit.
I'd still suggest you break it up some more. It's easy to add a few circuits now, while you can, instead of after the walls are done. As is, if that "purple" circuit breaker trips you have no lights in the "entertainment area" or "room 1" or either set of stairs.
Plan for the future, not today's loads. You may not have one now but how much power does a big Plasma TV take or a surround sound system need? I'd dedicate a circuit just for them and keep the lighting off of it. Do you have enough receptacles, spaced for Code? I see no receptacles near either set of stairs.
Code is the bare minimum. It does not mean that you can't do differently.
navid 06-08-2012 10:14 PM
Good suggestions :thumbsup: I will add more receptacles and breakers.
there are 5 free spots for breakers.
Ray103 06-12-2012 12:57 PM
my observation
Are you planning any electric in the utility room?
I think that the bathroom lighting should have a wall switch on the inside of the bathroom door, not outside. Other readers should/would know.