wiring off a gfi trips the circuit
Computer glitch---post removed as it didn't make sense
jim Pacini is offline   Reply With Quote
Old 01-25-2013, 10:35 PM   #2
wiring in a digtable light timer trips the GFI . help !!!
Old 01-25-2013, 11:50 PM   #3
UAW SKILLED TRADES
Stubbie's Avatar
Rewards Points: 2,652
Can you give a bit more detail...gfci receptacle or gfci circuit breaker? Plug in timer or hardwired timer? Is the timer wired off the load protection of a gfci receptacle etc..
Old 01-26-2013, 01:02 AM   #4
Oso954's Avatar
Rewards Points: 732
what make and model timer ?
Oso954 is online now   Reply With Quote
Old 01-26-2013, 07:32 AM   #5
Rewards Points: 1,440
If you connect anything to the "load" terminals of the ground fault interrupter unit then that portion of your circuit is a "subcircuit" that must not be connected to the incoming neutral or hot and must not be connected to the hot or neutral of another circuit.
The load terminals are not simply another pair of screws to hitch wires to. If two wires want to go under one screw, connect a short length (pigtail) to the screw and then connect the loose ends using a wire nut.
Be sure to connect the incoming feed to the "line" terminals, not the "load" terminals.
Do not connect the ground (green or bare) wire to the neutral (white) wire at any outlet box up in the houss. If you unhitch the ground wire from the timer and then everything works then your timer may be using ground for a neutral and that is incompatible for use with a GFCI and is also not code compliant in any situation.
Old 01-26-2013, 08:19 AM   #6
Electrical Contractor
kbsparky's Avatar
Some of those digital timers use the ground connection for internal neutral purposes. That type of imbalance can trip out a GFCI unit.
-KB
Wiring two switches, two lights, power from plug circuit TurboT Electrical 14 01-02-2013 09:25 AM
Wiring Size Calculations for New Service CorinthWest Electrical 7 12-07-2010 12:36 PM
trying to get educated about house wiring ChrisJJ Electrical 7 08-08-2010 03:23 PM
Replacing wiring in middle of run, ungrounded lighting circuit alexz Electrical 3 07-05-2007 09:53 PM