Wiring A New Timer - Electrical - DIY Chatroom Home Improvement Forum
Old 10-25-2010, 05:21 AM   #1
CG1
Wiring a new timer
I am have installed a new timer for my landscape lighting. It is different from the original timer and I am having trouble getting power. I will attach two pictures - I have installed the two jump-connecters per the instructions. I installed the power from the breaker to the left two posts. the lines feeding my landscape light are conencted to NC2 and NO2.
When I turn on the power the first few posts are hot but the left posts are not. Any help on wiring this correctly would be appreciated. thank you.
CG1 is offline   Reply With Quote
Old 10-25-2010, 06:25 AM   #2
Rewards Points: 756
Nice grounding connection. Why not just tie them in a knot?
busman is offline   Reply With Quote
Old 10-25-2010, 09:24 AM   #3
Licensed Electrician
It appears both the power and neutral are being switched. Try moving the wire currently on NC2 to NO.
Tuckahoe Sparkplug is offline   Reply With Quote
Old 10-25-2010, 11:32 AM   #4
CG1
Thank you, I appreciate the assistance and will try it this evening.
Old 10-25-2010, 03:32 PM   #5
Electrical Contractor
jbfan's Avatar
Rewards Points: 494
Lighting 120v?
Looks like to me that the neutrals tie together, and the NC2 sholud move to the NO.
Remove the jumper from the neutral to com2
As you have it wired now, the com2 does not have a hot wire.
jbfan is online now   Reply With Quote
Old 10-26-2010, 02:16 PM   #6
The manufacturer obviously intended to switch the neutral on one set of contacts and switch the hot with the other set. I'd leave the jumpers and neutrals as they are and just move the wire from NC2 to NO. Just my humble opinion.
Old 10-27-2010, 05:31 AM   #7
CG1
Hello again. My work has made other plans for me the past couple of days and I have not gotten home at a reasonable time to apply these suggestions. hopefully this evening !
Yes, 120V
I'll start with Tuckahoe's suggestions of moving the NC2 to NO and see what that nets me. If not I will remove the jumper as jbfan suggested as he too felt the NC2 should be moved. Like I said, if I get out of work at a reasonable time tonight I'll try these suggestions. thanks again !!
BTW, huge Jimmy Buffett fan here ;-)
Old 10-29-2010, 07:36 AM   #8
CG1
Hi all. Not pleased that work has been dogging me all week - but I was able to take today off ! Anyway, I switched NC2 to NO as Tuckahoe Sparkplug originally suggested and it resolved the issue - thank you all very much for your assistance, it's greatly appreciated !
Old 10-29-2010, 09:54 AM   #9
nap
You talking to me?
nap's Avatar
Rewards Points: 6,290
just for future reference;
always read the manufacturers instructions
when dealing with switches/contact;
NC= normally closed
NO= normally open
COM= common= generally associated with a set of other terminals a NO and an NC
this particular timer requires power to operate (the left 2 terminals) and is capable of switching two separate circuits if desired.
the neutral to the devices is not intended to be connected to the switched contacts.
so, if you are powering everything from one circuit, and that circuit is also used to power the timer, the connections should be (I cannot see the designations for the first two terminals so I will accept the neutral is in the proper position), I see that you are only controlling 1 device/circuit and you are using contact #2 so I will stay with that
terminal 1- circuit neutral, neutral to your controlled devices.
term 2 - circuit hot jumper to com 2 (you can also run a jumper to com if you need to switch an additional device
term 3- empty
term 4- empty
term 5- empty
term 6- empty
term 7- conductor to your controlled device(s)
term 8- jumper from term 2
the neutral to your devices can be inserted in term 1 or you can use a pigtail
Wiring an Intermatic Wall Timer in a three way switch aitutaki98 Electrical 6 07-23-2011 11:43 AM
Wiring an Itermatic Wall Timer in a 4 way stitch SunnyInFlorida Electrical 8 04-27-2011 11:15 PM
Mechanical timer wiring? Duane 70 Electrical 5 06-16-2010 08:57 PM
help wiring a timer in a 3 gang light box edadmartin Electrical 3 03-14-2010 08:05 PM
Help with digital timer wiring longman Electrical 7 12-06-2008 11:22 AM