Old 01-07-2010, 12:29 PM   #1
Question
wiring new GFCI breaker question
Hello DIY -
I am adding in a new 20amp circuit to my panel. This is for my garage and I will be using a GFCI breaker. My question is about wiring the breaker as the instructions are not very clear.
What I believe needs to be done; Is this correct?
  • I'll run 12/2 romex for this line to the panel
  • White and Neutral from the line attaches to the Neutral Bus Bar
  • Black (hot) wire attaches to the GFCI breaker
  • Curly white wire from GFCI breaker installs to the Neutral Bar
There is a second spot on the GFCI for another wire, what goes here? Do I pigtail the white from the line then attach to the bus bar?
Thanks everyone!
dgates12 is offline   Reply With Quote
Old 01-07-2010, 12:43 PM   #2
Electrical Contractor
The white from the 12/2 wires into the breaker, the curly white from the breaker wires to the neutral bar, and the black from the 12/2 wires to the breaker.
Yes I am a Pirate, 200 years too late. "Jimmy Buffett"
jbfan is online now   Reply With Quote
Old 01-07-2010, 12:48 PM   #3
Inspector/Instructor
codeone's Avatar
Originally Posted by dgates12 View Post
Hello DIY -
I
NO.
Your white wire on your 12/2 attaches to the other spot on your GFCI breaker.
The white wire from the breaker attaches to your neutral bar.
The white wire from your 12/2 is your neutral wire (grounded Conductor) the bare wire is your equipment grounding conductor.
Are you in a main panel or a sub panel?
codeone is offline   Reply With Quote
Old 01-07-2010, 12:48 PM   #4
Thanks JB.
Why couldn't the darn instructions that were packaged inside have been that simple?!?
Old 01-07-2010, 12:50 PM   #5
It's the main panel Codeone.
Thanks for the reply.
Old 01-07-2010, 12:52 PM   #6
codeone's Avatar
I should have looked at your pic closer would have known. In the main the grounding conductor and the grounded conductor(neutral) are tied together, in a sub panel they are seperate.
Old 01-07-2010, 01:00 PM   #7
Uh-oh Codeone, you may have lost me on that one. It sounds like your answer varies from what JBfan replied earlier or am I spacing out here?
  1. 12/2 ground {copper wire} --> to neutral bar (check)
  2. 12/2 hot {black wire} --> to GFCI breaker (check)
  3. Curly wire from GFCI breaker --> to neutral bar (check)
  4. 12/2 neutral (white wire} --> to GFCI breaker or pigtailed to neutral bar (umm??)
Old 01-07-2010, 01:12 PM   #8
codeone's Avatar
No JBfan is right the 12-2 white wire goes to the other slot on the breaker.
The White wire on the 12-2 is a grounded conductor or better known as a neutral. It does carry current.
The ground wire only goes to the neutral bar in a main panel.
If this was a sub panel the ground would go to the ground bar not the neutral bar.
The difference is grounded conductor= neutral.
The ground conductor is for equipment grounding and never carries current under normal conditions.
The grounded conductor (neutral) almost always carries current.
Therefore neutral is not a good name for the conductor but hte most common used.
Old 01-07-2010, 01:14 PM   #9
Gotcha...thanks!
15 AMP GFCI and breaker panel 8roty Electrical 6 01-04-2010 08:10 PM
code question - AFCI / GFCI breakers Red Squirrel Electrical 15 09-17-2009 12:16 PM
Older wiring question... PirateKatz Electrical 8 11-25-2008 11:11 AM
How to connect switch to GFCI breaker? firemanter Electrical 3 10-28-2008 08:46 PM
GFCI Question Nealndar Electrical 2 09-13-2008 06:15 PM