-   -   Wiring NEMA 6-50R (http://www.diychatroom.com/f18/wiring-nema-6-50r-141967/)
MisterSteve 04-29-2012 10:57 AM
Wiring NEMA 6-50R
I know this is beating a dead horse but I feel like I need some clarification. I will be installing a NEMA 6-50R Receptacle for a welder in my garage and I have figured out that I will not need the neutral from reading other posts here. But do I need to ground the receptacle box? I am using a metal Raco box.
itsnotrequired 04-29-2012 11:01 AM
are you running a new cable with an equipment grounding conductor? if so, ground the metal box the receptacle is located in.
MisterSteve 04-29-2012 11:09 AM
Yes, new cable, 6/3 NM. So if the ground is connected to the receptacle, how do I go about grounding the box?
Jim Port 04-29-2012 11:15 AM
The box should have a tapped hole for a 10-32 screw.
MisterSteve 04-29-2012 11:21 AM
Yep, I stuck a green ground screw in it. Do I then wirenut two pieces of bare #10? to the cable ground and attach one to the box and one to the receptacle?
itsnotrequired 04-29-2012 11:37 AM
install a pigtail on the receptacle and a pigtail on the box ground. wirenut the two pigtails with the ground in the cable. done.
MisterSteve 04-29-2012 11:41 AM
Got it. Duh. Thanks.
Speedy Petey 04-29-2012 03:31 PM
Leave the ground long, wrap it around the screw, then on to the receptacle. NO need for splicing.
kbsparky 04-29-2012 09:29 PM
You only need a 6/2 cable for a welder outlet. The neutral wire would not be used if you installed a 6/3.