Old 01-19-2011, 06:41 PM   #1
Rewards Points: 462
Wiring NEMA 6-15 with EMT conduit
Hello all!
Just want to verify the proper way to wire this 240V receptacle.
I am using EMT conduit and metal boxes run right to the panel so I assume the conduit & boxes will carry the ground?
Do I then only need to run the 2 hot wires through the conduit and use a pigtail to ground the receptacle to the box?
Just making sure I have this right. Thanks
Richo is offline   Reply With Quote
Old 01-19-2011, 06:46 PM   #2
Electrical Contractor
kbsparky's Avatar
Properly installed metal conduit systems do not need an additional equipment grounding conductor. What you described is correct.
Many folks recommend that you install a supplemental equipment grounding conductor -- especially when the conduit system is installed in wood-frame and similar structures.
-KB
Old 01-19-2011, 07:43 PM   #3
Rewards Points: 190
I just finished running a 240V line in EMT. It was a volunteer job in a local church but a retired licensed electrician was running the job. We ran a separate ground wire. He said it was required because EMT only has a set screw. If the conduit was threaded pipe a separate ground wire would not be necessary.
zircon is offline   Reply With Quote
Old 01-19-2011, 07:53 PM   #4
nap
You talking to me?
nap's Avatar
Rewards Points: 6,290
zircon, your retired electrician friend was incorrect. The setscrew is adequate for grounding means.
I prefer to install a separate equipment grounding conductor. I've seen too many times where conduit did come apart (although it was usually due to a forklift)
Old 01-20-2011, 12:33 AM   #5
Scared Electrician
Saturday Cowboy's Avatar
I am assuming that you don't need a neutral for this load. not if you're using a NEMA 6-15
Ragged Trousered Philanthropist
Please follow the code - its there for your safety no matter how inconvenient.
Saturday Cowboy is offline   Reply With Quote
Old 01-20-2011, 05:55 AM   #6
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,974
I FULLY agree on both points.
Speedy Petey is online now   Reply With Quote
Old 01-20-2011, 06:24 AM   #7
Rewards Points: 506
The original post stated 240v, so why assume?
jlmran is offline   Reply With Quote
Old 01-20-2011, 10:48 AM   #8
Rewards Points: 204
Don't for get the ground jumper from the box to the receptacle. Even with metal conduit, this jumper wire is required.
Old 01-20-2011, 08:56 PM   #9
Rewards Points: 462
Thanks for all your input. Gives me the answer I needed
Buried gas pipe in conduit WillK Plumbing 4 01-07-2011 12:50 PM
Wiring Lights and Running Multiple Circuits in Conduit mark_anderson_u Electrical 0 11-02-2010 09:06 AM
Basement wiring question kupalino Electrical 8 11-14-2009 09:25 AM
Cloth Wiring - Replace? JessicaGus Electrical 9 09-23-2009 06:45 PM
Knob & Tube wiring - How concerned should we be? hotdiggitydog Electrical 6 04-11-2006 07:52 PM