Old 05-28-2011, 06:05 AM   #1
Wiring a GFCI
I have 2 outlets in a laundry on the same dedicated circuit that are within 5' of the utility sink. 12/2 loops from the first to the second. Do I need each to be a GFCI or can I connect the second to the load terminal of the first? I am thinking that they both need to be GFCI because...and I may be wrong on this... if the second was not a GFCI and connected to the load of the first- if it came into contact with water it would not trip the first GFCI.
elmaur is offline   Reply With Quote
Old 05-28-2011, 06:11 AM   #2
Licensed electrician
Wiring a GFCI
You can wire both on the LINE side only or use a GFI in the first and use the LOAD terminals to wire a regular duplex receptacle as the second.
Old 05-28-2011, 06:13 AM   #3
BIGRED
Wiring a GFCI
Incorrect. If the first outlet after your fuse box or breaker box is a properly installed GFCI, all other outlets wired to that GFCI on the load terminals will be GFCI protected as well.
Grampa Bud is offline   Reply With Quote
Old 05-28-2011, 10:16 AM   #4
Electrical Contractor
Wiring a GFCI
It can be wired either way.
Use the line side only and put a gfci on both sides of the sink, or wire a gfci to the first spot, and use the load side to protect the next receptacle.
Just like Jim Port said.
Yes I am a Pirate, 200 years too late. "Jimmy Buffett"
jbfan is online now   Reply With Quote
Old 05-28-2011, 10:23 AM   #5
Wiring a GFCI
I notice that licensed electricians place a sticker on second outlet (and those in line after the primary obvious GFI outlet) that says 'GFI protected outlet' because they look like 'regular' outlets.
diyorpay is offline   Reply With Quote
GFCI Stumper ksqrdks Electrical 2 04-03-2010 07:24 AM
Wiring a Spa and THHN question. skleinsmith Electrical 29 04-02-2010 12:41 PM
Correct wiring of GFCI breaker Giles Electrical 8 02-23-2010 04:12 PM
GFCI between porch receptacles Thurman Electrical 4 08-19-2009 01:40 PM
GFCI intermittent nuisance trips jejm1975 Electrical 43 09-07-2008 10:18 AM