-   -   Wiring a GFCI (http://www.diychatroom.com/f18/wiring-gfci-105820/)
elmaur 05-28-2011 05:05 AM
Wiring a GFCI
I have 2 outlets in a laundry on the same dedicated circuit that are within 5' of the utility sink. 12/2 loops from the first to the second. Do I need each to be a GFCI or can I connect the second to the load terminal of the first? I am thinking that they both need to be GFCI because...and I may be wrong on this... if the second was not a GFCI and connected to the load of the first- if it came into contact with water it would not trip the first GFCI.
Jim Port 05-28-2011 05:11 AM
You can wire both on the LINE side only or use a GFI in the first and use the LOAD terminals to wire a regular duplex receptacle as the second.
Grampa Bud 05-28-2011 05:13 AM
Incorrect. If the first outlet after your fuse box or breaker box is a properly installed GFCI, all other outlets wired to that GFCI on the load terminals will be GFCI protected as well.
jbfan 05-28-2011 09:16 AM
It can be wired either way.
Use the line side only and put a gfci on both sides of the sink, or wire a gfci to the first spot, and use the load side to protect the next receptacle.
Just like Jim Port said.
diyorpay 05-28-2011 09:23 AM
I notice that licensed electricians place a sticker on second outlet (and those in line after the primary obvious GFI outlet) that says 'GFI protected outlet' because they look like 'regular' outlets.