-   -   Wiring Generator to Backfeed Breakers - Neutral and Ground Wires? (http://www.diychatroom.com/f18/wiring-generator-backfeed-breakers-neutral-ground-wires-148631/)
tjnoff 06-29-2012 04:25 PM
1 Attachment(s)
Hi! I'm planning on using an interlock kit (code approved model) when connecting my generator to my home's main power panel, as follows (drawing attached):
7500W generator (Generac GP7500E) with L14-30 generator cable connecting generator's 240V 30A outlet to an L14-30 inlet box (on house), then connect the inlet box to 30A dual-pole backfeed breakers in the primary power panel using 10/4 wire.
Backfeed breakers and main panel input breaker will be mutually exclusive using interlock (only one can be on at any given time).
My question is do I run both the neutral and ground wires from the inlet box to the neutral bus bar in this primary power panel, or just the neutral wire? If just the neutral wire, what's done with the ground feed? Anything?
One other secondary question: Are backfeed breakers unique from standard breakers? Do I need to find specifically backfeed breakers, or will your standard 30A dual-pole breakers work for this application?
Thanks for your help!
electures 06-29-2012 08:16 PM
What type of interlock device? Who makes it?
AllanJ 06-29-2012 08:29 PM
You would use an ordinary breaker for backfeed purposes.
The best way to arrange ground and neutral for a backfed generator is to unbond the neutral from the generator's frame and ground connection inside the generator. Occasionally this cannot be done easily in which case I would be tempted to leave the green wire unhooked somewhere in the wiring between panel and generator. I would not mutilate a generator to get its neutral and ground unbonded.
brric 06-29-2012 08:54 PM
Connect the neutral and the ground wires from the generator to the load center. DO NOT tamper with the generator.
stickboy1375 06-29-2012 08:57 PM
12 Attachment(s)
If you cannot remove the N-G bond at the generator, then you must switch the grounded connector at the transfer switch.
brric 06-29-2012 09:05 PM
And why would that be?
stickboy1375 06-29-2012 09:27 PM
12 Attachment(s)
You can only have one point where your N-G are bonded together.
brric 06-29-2012 09:32 PM
What do you think would be the consequences? It works fine on my personal home and others I have done.
andrew79 06-29-2012 09:39 PM
A generator is not considered a permanent part of the electrical system. Removing the bond in the generator voids the warranty. Also if the generator is used for anything other than back feeding the house it could be potentially dangerous with the bond removed.
Oddly enough this is one of the reason a genny panel switches out the neutral that you argued so much about not needing.
brric, what's you've in essence done is run a ground and a neutral in parallel with each other, in theory they can both carry some of the current.
stickboy1375 06-29-2012 09:43 PM
12 Attachment(s)
Its a code violation, plain and simple. And just because it works, doesn't make it correct.
brric 06-29-2012 09:44 PM
That is correct. It is a temporary plug and cord connection. It is not intended to be permanent. Also, removing the bond would create a possible generator fault clearing issue.
stickboy1375 06-29-2012 09:45 PM
12 Attachment(s)
I didn't argue anything, I told you current doesn't seek the earth. :)
andrew79 06-29-2012 09:46 PM
i should have clarified, only the last bit of that post was directed at you brric, the first was for stickboy.
never thought of the fault issue, good point.
stickboy1375 06-29-2012 09:46 PM
12 Attachment(s)
And is still a violation. :)
stickboy1375 06-29-2012 09:47 PM
12 Attachment(s)
I know. :)