Wiring Detached Pole Barn - Electrical - DIY Chatroom Home Improvement Forum
Old 06-16-2011, 05:02 PM   #1
I am wiring my pole barn (detached, obviously), mostly for lights and basic electircal needs (no significant loads). I already ran conduit from the main box in the house to a 100 amp panel in the garage, a distance of 110 feet total. I had a 500 Foot spool of THHN/THWN #6 and ran 4 strands through the conduit. I intend to have two "hots" (Black/Red), one neutral (white), and one ground (green). I intend to put in a 40 amp in the house and back feed a 40 amp in the barn. There will be one circuit for lighting and two for outlets. In the barn panel, would it be proper to: Backfeed the circuit breaker with the red and black; Attach the white to the neutral bar(which will not be bonded to the ground or panel); and Attach the green to the ground bar? Do I need ground rods? There are no other connections from the house to the barn.
wparker is offline   Reply With Quote
Old 06-16-2011, 05:30 PM   #2
A "Handy Husband"
rjniles's Avatar
Rewards Points: 4,142
Curious on how you are getting red, black, white and green out of a 500 foot spool of THWN?
Coastal South Carolina
Old 06-16-2011, 05:32 PM   #3
Electrical Contractor
kbsparky's Avatar
Sounds about right. You will have to install ground rods at the outbuilding, and bond them to your green conductor in the sub-panel.
As for backfeeding the 40 Amp breaker, this is permissible as long as that breaker has a retaining kit installed to prevent it from accidentally being unplugged while energized.
-KB
Old 06-16-2011, 06:55 PM   #4
Electrician
SD515's Avatar
Rewards Points: 504
Good call rj. You can't re-color #6 in conduit.
Kyle
Old 06-17-2011, 07:34 AM   #5
Thank you for the replies. The wire is red. I taped the ends in each box the corresponding black, white and green - the entire length that was in the box. I will insert the ground rods and secure the backfed breaker. Thanks again.
Old 06-17-2011, 08:08 AM   #6
A "Handy Husband"
rjniles's Avatar
As SD515 stated, it is a code violation to remark wire #6 or smaller. Your inspection will fail and you will have to rerun. Avoid all that and get the correct color THWN
The Following User Says Thank You to rjniles For This Useful Post:
SD515 (06-17-2011)
Old 06-17-2011, 06:09 PM   #7
Electrician
SD515's Avatar
Rewards Points: 504
And you would only have to change the white and green. It's ok to use the red for the 2 'hot' legs, you don't have to re-color them.
Kyle
Old 06-17-2011, 08:24 PM   #8
kbsparky's Avatar
A stupid rule that has little basis in safety. The tape doesn't care whether the wire is a #6 or #4. Some inspectors won't have a cow over #6 that has been taped on the ends, either. Your mileage may vary.
-KB
Old 06-17-2011, 09:06 PM   #9
Electrician
SD515's Avatar
Rewards Points: 504
True. I would suspect manufacturers had a hand in that rule. You’re right, the tape doesn’t care what it’s attached too. I know the electrons don’t care what color the wire is. But rules are rules…I didn’t write ‘em…just have to follow ‘em. Just trying to point 'em out.
Kyle
Pole barn vs steel I beam building. Do they compare structurally? viper Building & Construction 0 05-23-2011 07:17 PM
Building a basic pole barn fjacky Building & Construction 2 03-02-2010 10:58 PM
wiring 100A to detached garage snowman Electrical 4 11-28-2009 05:53 PM
Pole Barn Girts, etc... DonAK Carpentry 1 08-16-2007 10:06 PM
Wiring a Pole Barn rocky Electrical 8 02-02-2006 07:34 PM