Wiring For Detached Metal Bldg - Electrical - DIY Chatroom Home Improvement Forum
Old 06-23-2011, 04:06 PM   #1
Wiring for Detached Metal Bldg
My father in law had a metal shop built. Metal framework and sheet metal roof and sides. Now he wants me to help him run electricity to it. They did not install a ground rod through the slab, but did stub up for electrical conduit. Here is my thoughts and let me know if this is correct. Connect 6/3 UF wire to 60 amp double pole breaker in the house breaker panel. Run in PVC conduit underground to new breaker panel. Remove bonding screw. Install grounding rods outside of Bldg. Connect wire from Ground rod to Ground buss. There will be no other lines connecting the buildings.
Here's my questions. Does the Ground wire to the rod needs to insulated or not? If I leave it uninsulated it will it bond the building to the ground. Should I install the service panel on 2x4's or can it touch the metal studs? I plan on using metal junction boxes and rec. boxes, Is there any special attention needed for those?
splittoe is offline   Reply With Quote
Old 06-23-2011, 04:47 PM   #2
Licensed electrician
Rewards Points: 1,750
You could sleeve the UF where it enters and exits the ground. There is no need for UF to be in conduit unless to protect from physical damage. Individual conductors in conduit is much easier.
Yes you will need a ground rod at the outbuilding. The grounding conductor does not need to be insulated.
Old 06-23-2011, 04:56 PM   #3
Yeah I forgot about THWN wire. What size will the ground need be in the conduit?
Old 06-23-2011, 07:29 PM   #4
Electrician
SD515's Avatar
Rewards Points: 504
At least #10 copper, green or bare. I don't like pulling bare wire in conduit, but #10 isn't that bad for a short run.
Kyle
Old 06-24-2011, 07:55 AM   #5
Will I still need to ground the metal boxes, if I'm screwing it to metal studs? What about the breaker panel can it be mounted to the metal studs or does it matter?
Old 06-24-2011, 11:50 AM   #6
Rewards Points: 204
Yes. You need a pig tail from the metal box to the receptacle. Screwing the panel to the metal studs is fine. However, I would use a back board. This way you have a way to secure the conduits or cables as they leave the panel.
Old 06-30-2011, 11:17 AM   #7
So will it be ok installing the panel to the metal framework of the building? Or does it need to be framed out with 2x4's?
Old 07-14-2011, 08:17 AM   #8
Rewards Points: 340
correct pipe
does the exposed pipe to the outlet box need to be schd 40 or emt?
kt82 is offline   Reply With Quote
Old 07-14-2011, 05:39 PM   #9
Electrician
SD515's Avatar
Rewards Points: 504
Please explain more about what you are doing.
Kyle
Old 07-14-2011, 10:35 PM   #10
Missouri Bound's Avatar
You will need 4 wires from the main panel as you must pull a ground as well with the circuit. And in the sub panel you will need to isolate the neutral buss from the panel, and bond the grounding buss to the panel. And the grounds and the neutrals need to land on their respective buss. The length of the run will determine the circuits wiring size at any given ampere rating.
Old 07-15-2011, 01:22 AM   #11
Does a subpanel pull only how ever many amps are available from the single slot?
design_lover13 is offline   Reply With Quote
unsafe wiring to shed? lawsklsux Electrical 7 11-14-2010 12:16 PM
Unusual three way switch wiring help r1racer Electrical 9 11-11-2010 08:49 PM
electric wiring in house remodel wis_remod Electrical 6 04-02-2009 02:40 PM
Knob & Tube wiring - How concerned should we be? hotdiggitydog Electrical 6 04-11-2006 07:52 PM
Garage - Protecting wiring installation eastment Electrical 4 11-26-2005 11:52 AM