-   -   Wiring Detached Garage for 220v welder (http://www.diychatroom.com/f18/wiring-detached-garage-220v-welder-66525/)
8N1949 03-11-2010 09:15 AM
This forum looks to me the right place to get some answers. Here goes,
I just purchase a Mig welder with 220v. The label on the welder states..Standard NEMA 6-50P 50Amps 220 volt. 220VAC Single Phase. Use 50 AMP Power Source with 6-50R.
In the main garage I have a 200 AMP panel. From the main panel to the "sub-panel", I have 4-#6 wire (Red, Black, White, and Green) The Red and Black is attached to a 50 amp 2 pole Square D circuit breaker. The 4-#6 wires run in a 1-1/2" gray conduit two feet under ground some 23 feet total to the "sub-panel" in the detached garage. The sub-panel has 6 shots for breakers.
I have four of those with 20 amp breakers for lights, garage door openers, etc. The two open slots will be for the 50 amp 2 pole breaker for the Mig Welder.
Here's what I have so far. The plug on the welder power cord in 3 prong 6-50P with red, black, and Green/yellow stripe (ground). I have the wall box with a 6-50R (receptacle. I intend on running 3#6 wires (red, black, green) from the 50 amp 2 pole breaker to the 6-50R (receptacle).
Question> Is this the correct way to complete the setup?
Thanks for your expert advice.
jbfan 03-11-2010 09:24 AM
Sounds good to me.
You could change the breaker in the main to 60 amps if needed.
brric 03-11-2010 09:47 AM
You could use two #6 for the hots and a #10 for the equipment ground(green).