I am putting in a new kitchen for my inlaws. I ran all of the electric this weekend. I am putting in under-cabinet lighting. I got 3 dimmable xenon lights that will all be controlled by the same dimmer switch. This is the way I ran them:
ran homeruns for all 3 lights into the same box tied together all neutrals (white) at the dimmer switch box (4 wires - 3 lights and source power)) tied all grounds at the dimmer switch box (5 wires - 3 lights, input power, switch) tied all switched hot (black) at the dimmer switch box dimmer output (4 wires - 3 lights, switch output) tied input power (black) to dimmer input (2 wires) Essentially I ran this like you'd run 1 light fixture accept I tied all three together. I did this to avoid having any burried junction boxes (against code) by running the wires from switch to switch. Is this wiring scheme ok? I could not test since none of the power is tied into the breaker box yet. |
#2 |
Licensed electrician
I am concerned about the size of the junction box you have installed. Even if you installed #14 wires you would need a 22 cubic inch box as a minimum. If you installed #12 it would need to be 27.5 cubic inches.
You may have trouble trying to fit the dimmer into the box too.
Answers based on the National Electrical Code. Local amendments may apply. Check with your local building officials. |
#3 | |
Is this wiring correct??Quote:
Is the wiring scheme acceptable/code? |
#4 |
Your wiring scheme sounds fine. I was just worried about the box size.
The grounds from both circuits need to be spliced together and go to both the GFI and dimmer.
#5 |
Thanks Jim - The GFI and the dimmer share 1 20 amp circuit using 12/2 wire. The wire comes into the GFI and the dimmer gets power from the "load" terminals of the GFI outlet. Is that ok? These are the only 2 things on this circuit (GFI and 3 xenon lights).
#6 |
If this is a 20 amp small appliance circuit in the kitchen you cannot supply anything except receptacle loads. The lighting would need to be fed from another circuit.
#7 |
Well that sucks. Is this a safety issue/code? I knew that you weren't supposed to run lights and outlets on the same circuit but I thought this was just "best practices" and not code.
#8 |
This is a code issue. Certain circuits like small appliance kitchen, bathrooms and laundry circuits are more restricted than other general use circuits.
| Display Modes | |
| How to test wiring insulation? | Shea_Close | Electrical | 13 | 08-25-2010 04:55 PM |
| Cooktop and Stand Alone Oven Wiring Replacing Existing Single Range/Stove Combination | ffauth | Electrical | 3 | 08-23-2010 10:03 PM |
| Wiring Problems | sunici | Electrical | 18 | 04-26-2009 09:27 PM |
| electric wiring in house remodel | wis_remod | Electrical | 6 | 04-02-2009 03:40 PM |
| Knob & Tube wiring - How concerned should we be? | hotdiggitydog | Electrical | 6 | 04-11-2006 08:52 PM |