What size wire and what size/type of breaker should be feeding a 2 1/2 ton a/c unit?
schultz56 is offline   Reply With Quote
Old 02-15-2010, 12:46 PM   #2
Rewards Points: 320
Look at the nameplate rating on the unit to be sure. I have a 2.5 ton and it takes a 30 amp circuit and #10 wire.
teamo is offline   Reply With Quote
Old 02-15-2010, 12:56 PM   #3
PA PE
Is it safe to say that you should use:
14 gage wire for 15 amp curcuit
12 gage wire for 20 amp
10 gage wire for 30 amp?
Old 02-15-2010, 01:22 PM   #4
Licensed electrician
Rewards Points: 1,766
The wire sizing rules for air conditioning compressors are different than regular branch circuits. Check the nameplate for the minimum circuit ampacity for the wire size and the maximum overcurrent protection to size the breaker.
Old 02-15-2010, 01:50 PM   #5
This topic was recently discussed over here...
A/C Electrical
That should help you determine the correct wire size, and as teamo pointed out, you have to start with what is on the side of the A/C unit rather than based on generic size of the unit.
HooKooDooKu is offline   Reply With Quote
Old 02-15-2010, 03:03 PM   #6
PA PE
I will just read the data panel on the unit. Thanks all.
Bathroom light/exhaust fan/heater wiring Redlos Electrical 39 10-31-2009 04:21 PM
Quick HVAC / sump pump wiring question MattOverMinder Electrical 4 01-23-2009 07:42 AM
Electric question from power pole to unit Slocalaman Electrical 3 11-06-2008 03:23 PM
Bathroom Fan/Heater unit incompatible with electric wiring? bathroom nightmare Electrical 4 02-09-2008 03:41 PM
Knob & Tube wiring - How concerned should we be? hotdiggitydog Electrical 6 04-11-2006 07:52 PM