Wiring Basement Lighting - Electrical - DIY Chatroom Home Improvement Forum
Old 07-16-2009, 11:57 PM   #1
wiring basement lighting
I'm finishing the basement...... I already modified some wiring (separated ceiling lights into 2 separate circuits with their own switches). The utility area is powered back up and working with the newly located switch. The other lights in the finished area have been removed and have been replaced with canned lights. I have return air through floor joists so I can't take the shortest route between the canned lights, rather than run a bunch of wire to a canned light and back to continue to the next, can I branch off 2 or more lights off of 1 light? See attached basic diagram.
Second, I made a half-wall at the bottom of the stairs into the basement. The 3-way switch had a wire going up to a light at the bottom of the stairs, this light is in a finished ceiling area so I cannot remove to replace with a longer length of wire. With the half wall I had to run-out the wire further and now the wire cannot reach the exisiting 3-way switch. It can however reach the wiring box for a new smoke detector so I ran the wire there and then extended it to reach the switch. Is this allowed, I'd rather do this than have a junction box.
Thanks in advance for anyone's advice and help.
8roty is offline   Reply With Quote
Old 07-17-2009, 06:42 AM   #2
Electrical Contractor
kbsparky's Avatar
Too many wires in that first can light.
Yes, you can hide a splice in the back of the smoke alarm box, provided you have sufficient cubic inch volume for all the conductors.
-KB
Old 07-17-2009, 08:07 AM   #3
300zx's Avatar
Post
Run 3 wire between the two three ways and then one out to light 12-2 then light to light.And power to switch box not to can to many wires in there.
300zx is offline   Reply With Quote
Old 07-17-2009, 11:14 PM   #4
Do I understand correctly, I need 12-2 wire to go to the first can light from 3-way switch #2? Is 14-2 wire sufficient to run from light to light? And must I run wire from light to light in series or can I branch off from one can light to power 2 different runs of lights connected end to end?
Thanks again!
Old 07-18-2009, 12:55 AM   #5
You use #12 wire throughout the circuit if it is protected by a 20 amp breaker, use #14 throughout if it is protected by a 15 amp breaker.
You should be able to branch from one light to 2 seperate runs if there is room in the attached junction box.
KeithM62948 is offline   Reply With Quote
Old 07-18-2009, 10:09 AM   #6
your putting power at the light and the three ways are dead end are you ok on that its a little different so im just asking i can tell you how and you look in the box on the can an see how many wires or how many cubic inches it says
javier is offline   Reply With Quote
Old 07-23-2009, 07:49 PM   #7
I can re-run the wire to have switch#1 to switch #2 to the can lights. However, is the diagram I posted OK??,..... it sounds like from the responses that there are too many wires in that first can light. The interior of the can light reads: MAX OF 8 NO. 12 AWG (4 IN 4 OUT) THROUGH BRANCH CIRCUIT CONNECTORS.
Does this mean that running 2 14-3 and 2 14-2 wires into that box is OK?
Old 07-23-2009, 08:04 PM   #8
basement
the truth is no if it holds 8 #12 wire that means that box is 18 cubic inches when calculating 14 wire you multiply by two so you have 2 #14-3 so that is twelve cu in then you have 2 #14-2 witch is 8cu in and then the ground is 2 so you have 22cu in
Old 07-23-2009, 09:01 PM   #9
Thanks for the explanation, at first i was really confused with the numbers and calculation but I think I understand it now. So 3 #14-2 wires in a light (1 incoming, 2 outgoing if I make a branch to 2 separate runs of lights) would total 14 cu in?
Old 07-23-2009, 09:26 PM   #10
Here is an updated diagram, everything check out OK?
Old 07-23-2009, 10:38 PM   #11
Much better. The boxes will be less crowded and you will only need one 14-3 cable.
jovingo is offline   Reply With Quote
Old 07-24-2009, 06:52 AM   #12
looks good and easy
Old 07-25-2009, 11:07 AM   #13
When I use an existing box with enough sq in to make a separate connection to extend another run, do the grounds from both runs need to be connected together in the box? I connected them separately but I think I saw somewhere that they should be connected together.
Old 07-25-2009, 11:40 AM   #14
Tie all grounds together and make sure the grounding conductor is also bonded to the box if it is a metal box.
Old 07-25-2009, 07:00 PM   #15
New Home Owner
For the breaker in a basement application such as this one, should a 15A GFIC be used instead of a normal 15A breaker?
DandHJohn is offline   Reply With Quote
Wiring for half bath in basement ELurie Electrical 5 08-06-2011 10:06 PM
Wiring a basement Jeffrey262 Electrical 7 06-30-2009 04:59 PM
basement wiring plans for lights JonnyG Electrical 10 04-05-2009 06:46 PM
Basement wiring hotrod Electrical 17 07-14-2006 08:01 PM
Installing new lighting on knob and tube wiring drichard Electrical 1 03-05-2006 03:55 PM