Wiring A 220v Dryer Receptacle - Electrical - DIY Chatroom Home Improvement Forum
Old 06-03-2007, 07:16 PM   #1
Wiring a 220v dryer receptacle
I have a Nema 10-30 receptacle (3-slot) for a dryer that I am installing. I have the 10-3 wire run, and I know that the black and red wire connect to the two hot posts (slanted slots) and the white wire connects to the neutral (L-shaped slot). The receptacle has no connection for ground. I figure, since dryers with three prongs typically have the neutral and ground tied together inside the machine, that I just connect the unshielded ground wire to the same screwpost as the neutral.
Is this correct?
pjpjpjpj is offline   Reply With Quote
Old 06-03-2007, 07:22 PM   #2
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,882
Is this a new circuit or replacement? You CANNOT use that receptacle for a new installation. You MUST use a 14-30 4-wire receptacle.
Old 06-04-2007, 07:25 AM   #3
It's new. Why do they sell this thing at the store then? Just for remodels? Ugh. So the 14-30 has the same plug slot arrangement? Or am I going to have to get a new cord for the dryer too? There's already one (10-30) in my house, original to the house (1987).
Old 06-04-2007, 07:36 AM   #4
Yes they sell them just for direct replacements.
Yes you need a new dryer cord.
The existing is fine it is grandfathered in till do you need to replace the cable.
Master Electrician
jwhite is offline   Reply With Quote
Old 06-04-2007, 12:08 PM   #5
Rewards Points: 530
What does the 14 signify, Petey? Not wire gauge, surely. Do the new dryers still have the ground strap going from the case to the ground post on the dryer? If so and he ever goes to change the wiring to 4 wire, he should replace the strap and attach the green ground wire in its place. Correct me if I am wrong on that.
Old 06-04-2007, 01:50 PM   #6
New dryers do not have the bond strap, they come with a four wire cord.
14 is the line number on the NEMA configuration chart. All 14s are 250volt single phase with neutral and ground. (4 prongs total)
Master Electrician
Old 06-05-2007, 12:59 PM   #7
Thanks for the info guys - I'll be returning the receptacle and buying a new cord and receptacle tonight. (sigh)
So, just curious, how were the old ones wired then? 10-3 wire and both ground and neutral from the same post (as I originally guessed)? Or was the house just wired with 10-2? Seems kinda sketchy to me....
Old 06-05-2007, 02:04 PM   #8
Licensed Pro
The only acceptable way dryers (and ranges) could be wired with three conductors was by using three insulated wires (such as 10/3 without ground) or by using SE type cable. Using a bare wire for the neutral/ground has never been an acceptable practice.
Old 06-05-2007, 05:08 PM   #9
Master Electrician
JohnJ0906's Avatar
The code changed in '96 (I think) to require separate neutral and ground for dryers and ranges. Prior, the frames were grounded through the neutral. This is still legal for EXISTING installations only. (Grandfathered in). If a new circuit is run, it must have 4 wires, hot, hot, neutral, ground, with a 30 amp, 120/240v w/ ground receptacle.
John from Baltimore
One Day at a Time
"Experience is what you get when you were expecting something else"
"The bitterness of low quality lingers long after the sweetness of low cost is forgotten"
JohnJ0906 is offline   Reply With Quote
Dryer wiring jasjks Electrical 8 09-11-2006 05:33 PM
Location of 220 and 110 outlets for dryer and washer JAJJ Electrical 2 08-07-2006 10:16 PM
wiring for a dryer irish_hood Electrical 4 01-11-2006 02:27 PM
Split Receptacle on 3-Way Circuit NPS Electrical 6 11-03-2005 10:28 AM
wiring an electric receptacle Jonathan_in_KY Electrical 2 01-05-2005 10:28 AM