Old 09-21-2008, 01:24 PM   #1
wire sizing for wall heater?
I am installing two wall mounted convection heaters. One is 500 watts and the other is 1000 watts. I am trying to determine what gauge wire I should be using. I can not find any information on amperage. The instructions say to install it with 240 volt wire. The folks at the electrical supply said 14 but to play it safe 12 gauge. I have a book that says for 240 volts you should use 10 gauge wire and then in the same book it talks about installing a 240 volt baseboard heater and using 12/2 wire.
So I'm a bit confused! I have the 12/2 and am half way through installing the first one!
Thank you.
G
gerhops is offline   Reply With Quote
Old 09-21-2008, 01:29 PM   #2
Electrician
Watts/Volts=Amps
1500W/240V=6.25A
So you would be good with 14/2 on a 2pole 15A breaker.
So your fine with your 12/2 on a 15 or 20A breaker.
darren is offline   Reply With Quote
Old 09-21-2008, 01:41 PM   #3
Thank you!
Old 09-21-2008, 02:08 PM   #4
Electrician
Originally Posted by darren View Post
Watts/Volts=Amps
1500W/240V=6.25A
You forgot to add 125% for electric heat.
chris75 is offline   Reply With Quote
Old 09-21-2008, 03:14 PM   #5
Send a message via AIM to theatretch85
By my calculation, 6.25 + 125% = 14.0625 amps. 80% of a 20 amp circuit would be 16 amps, so a 20 amp circuit would be adequate for the 2 heaters to be running at full. Good choice going with the 12 gauge wire instead of the 14! Definitely a very wise decision; its always better to have a little bit too large of a wire than not large enough!
theatretch85 is offline   Reply With Quote
Old 09-21-2008, 03:24 PM   #6
Electrician
Why are you adding 125% yet still using only 80% of a breaker? WAY OVERKILL!!! A 15 amp breaker is perfectly fine.
Old 09-21-2008, 03:27 PM   #7
Why are you adding 125%?
jerryh3 is offline   Reply With Quote
Old 09-21-2008, 03:28 PM   #8
Electrician
You have to for electric heat, the problem is why is he only using 80% of the breaker.
Old 09-21-2008, 03:31 PM   #9
Sorry, my bad; I don't do electric heat installations. Besides, last time I checked, a 15 amp breaker costs the same as a 20 amp breaker. He already has 12 gauge wire run, so connecting it to a 20 amp breaker wouldn't be an issue.
Old 09-21-2008, 03:34 PM   #10
Electrician
The only rule is that you have to add 125%, but the reciprocal is 80%, but no need to do both.
Old 09-21-2008, 03:36 PM   #11
210.19? If this is the only thing on the circuit, wouldn't it only need 125%(of the continuous load) protection?
Old 09-21-2008, 03:37 PM   #12
Thanks, now I will know for the future in the event I ever have to deal with an electric heat install.
Old 09-21-2008, 03:40 PM   #13
Electrician
wouldn't it only need 125% protection?
Correct... my mistake if you misunderstood me.
Old 09-21-2008, 03:42 PM   #14
Electrician
The Code reference is 424.3(B)
Old 09-21-2008, 04:05 PM   #15
Electrician's Helper
Pudge565's Avatar
Send a message via AIM to Pudge565
First off show ever said 14.xxx amps is wrong the math is 1500/240=6.25 amps them you need 125% so 6.25*1.25=7.8125 so a 15 amp breaker is way more than enough but you can put it on a 20 amp breaker if you so desire.
Pudge565 is offline   Reply With Quote
Tags
gauge, heater, volts
How to wire a US tankless water heater in Italy The Duck Electrical 1 09-04-2008 10:18 PM
how to wire an electric heater murray59 Electrical 8 04-26-2008 12:21 PM
Sizing a hot water heater. Randell Tarin Plumbing 2 01-26-2008 06:02 PM
Baseboard Heater: Can I wire it to plug into an AC recepticle? JBiz Electrical 3 12-01-2007 09:42 AM
Help with wire sizing pdxoregon Electrical 2 08-17-2006 08:15 PM