-   -   Wire sizing (http://www.diychatroom.com/f18/wire-sizing-20124/)
rtyui2 04-20-2008 09:08 AM
Wire sizing
Good morning,
I want to install a sub-panel in my shop. I have a 100 amp, GE model. Can I use 6-3 wire from my main panel to the new sub-panel?
Mike
joed 04-20-2008 09:32 AM
You can if you use a 60 amp breaker.
Speedy Petey 04-20-2008 09:32 AM
Yes. Depending on the distance you can breaker this at no more than 60A in the main panel.
The 100A panel is just the maximum rating. You can feed it with 60A, or less.
micromind 04-20-2008 11:56 AM
The above posts are exactly correct, I'd like to add; is this wire a 6/3 with ground? To feed a subpanel, you need 2 hots, 1 neutral, and 1 ground. 4 wires total.
Rob
mr500 04-21-2008 04:29 PM
Originally Posted by rtyui2 (Post 117687)
Good morning,
Mike
I just finished this project this weekend. I used #3 and #8 for Eq ground. Let me tell you that #3 kicked my A#^. BUT if you want more amps you have to up the wire size. I was going to go with a 60 amp, but decided as long as im running conduit and things might as well run bigger wire for 100amp and thats what I did.
Just know that the ground and neutral have to be separated (different busses) AT the sub panel. I had to go buy and equipment ground buss for my GE box seeing how it did not come with one. But there available. everywhere.