Wire Size Vs Breaker Size - Electrical - DIY Chatroom Home Improvement Forum
Old 08-20-2011, 09:16 AM   #1
wire size vs breaker size
I have an existing 240v circuit with 8-3 cu wire (not in use). It requires a 50a breaker, but I would like to use this for a 30a generator, that backfeeds back into my 200a panel that is equiped with a 30a generator throw switch.....question is, due to size of wire (8/3), can I install a 30a outdoor gfci for the backfeed, or do I need to install new 10-3 wire? Thanks
Jimster 481 is offline   Reply With Quote
Old 08-20-2011, 09:41 AM   #2
A "Handy Husband"
rjniles's Avatar
Rewards Points: 4,034
Yes you can use an over sized wire wire for a smaller load. However I do not think you can back feed a GFCI.
Coastal South Carolina
Old 08-20-2011, 09:43 AM   #3
Code05's Avatar
Rewards Points: 1,104
You cannot back feed a regular receptacle from a generator. You would need a suicide cord to do so. NOT GOOD!!!!!
Get a proper inlet.
Code05 is offline   Reply With Quote
Old 08-20-2011, 10:41 AM   #4
Rewards Points: 1,418
You can replace the receptacle at the end of that 8-3 gauge line with a male receptacle (inlet), also replace the breaker with a non-GFCI double breaker. You must put an interlock system on the panel so both the breaker for that 8-3 circuit and the main breaker cannot be on at the same time.
In localities where cam-lever panel interlocks are not permitted, the transfer switch must be in the feed line for the main panel. This can require coordination with the power company to pull the meter when you are installing this tranfer switch.
If all of the circuits eligible to get generator power are in a subpanel, this 8-3 line can be rewired to a transfer switch in the feed from the main panel to the subpanel.
20A Breaker, 14 gauge wire? joside Electrical 12 08-25-2010 10:41 AM
Size wire for A/C, A/H and Range? tripflex Electrical 6 06-07-2010 11:38 AM
Size of Wire & type of wire agman Electrical 6 11-10-2009 09:13 PM
Wire Needed for GF / Arc Fault breaker jamiedolan Electrical 13 09-20-2009 09:15 AM
wire size for ac/heating forced air unit macfluke Electrical 2 03-04-2009 01:29 AM