Wire Size Suggestions - Electrical - Page 2 - DIY Chatroom Home Improvement Forum
Old 10-19-2008, 03:05 PM   #16
Electrician
Originally Posted by rgsgww View Post
Your supposed to have a means of disconnecting the entire multiwire circuit at once, so you go with a double pole breaker as an easy way of doing so.
The disconnect has to be at the detatched structure.
Not to mention the requirement of physical protection of the wire and how you have to dig 24" deep if you go the romex way, 18" if you go with conduit.
This is not true, first off, you cannot use NM type cable, it would have to be UF, but certain rules apply that you just dont understand. here are the correct rules...
chris75 is offline   Reply With Quote
Old 10-19-2008, 04:04 PM   #17
That is what I meant, I probably should have described it better.
I always thought that uf was a type of romex, I know it is required in direct burial situations, wet locations, etc. and that type nm isnt allowed.
Thanks for the rules, I should have looked in the nec first, was in a hurry.
rgsgww is offline   Reply With Quote
Old 10-19-2008, 04:09 PM   #18
Romex would be illegal to run underground, even if it is run in conduit. You must run UF (underground feeder) or conduit the entire run with individual THWN wires in the conduit.
Again, at my last post, I always thought that UF was a type of romex. I do know it is illegal to use type nm.
I was thinking of a different switch yes, a double pole switch would be good.
hooking up dryer....bronx ny code SURFBUG Appliances 6 10-14-2008 09:41 PM
Aluminum wire size/ guage / amps? walt1122 Electrical 17 07-30-2008 10:44 AM
Wire size and Breaker size for remodel ?? Skydmark1 Electrical 12 12-15-2007 05:00 PM
Wire size for distance Question fburke Electrical 4 07-28-2007 09:29 AM
wire size wire to 10kw furnace? lochcarron Electrical 1 04-10-2005 07:43 PM