Wire Size Question - Electrical - DIY Chatroom Home Improvement Forum
Old 05-11-2012, 08:07 PM   #1
Wire Size Question
I have a barn that I need to run a feeder wire to from a 200 amp meter base 100 feet from the panel in the barn, the barn has a 125 amp main lug 4 circuit 4 space panel in it now.
the 200 amp meter base has no other use but the barn. I have approx 20 lights, a small fridge, air comressor and a well pump that is approx 500 feet from the barn and 300 ft deep
what size wire do I need to run from the meter base to the panel in the barn
thanks much
Ridgerunnertc is offline   Reply With Quote
Old 05-11-2012, 08:13 PM   #2
Missouri Bound's Avatar
See if this helps.Wire Size Calculator...............
Do you want it your way or the right way?
Old 05-11-2012, 10:02 PM   #3
Master Electrician
would need to know what the amperage is for the well pump. Basically from what little i know of the NEC i believe that feeders are rated to 3% votage drop and branch circuits are rated to 3% voltage drop. The two combined can't exceed 5% to the furthest branch circuit. Having said that if the voltage drop is a go then you'll need a #3 copper for a 100A main breaker and #2 if it's a 125A main breaker.
Sarcasm is my friend
I'm here to learn too, i do mostly commercial/industrial/new construction and this place is a great way to pick up tips on residential from some good electrical minds. Excuse the spelling, my phone has a mind of it's own.
andrew79 is offline   Reply With Quote
Old 05-12-2012, 06:51 AM   #4
Code05's Avatar
Rewards Points: 1,104
While a good idea in many cases, except for fire pumps and sensitive electronic equipment wired off a 60/120 transformer, the NEC does not require you to adjust/compensate for voltage drop.
It is only recommended.
Code05 is offline   Reply With Quote
Old 05-12-2012, 07:04 PM   #5
Master Electrician
Section 215-2(b) FPN No. 2. Conductors for feeders as defined in Article 100, sized to prevent a voltage drop exceeding 3 percent at the farthest outlet of power, heating, and lighting loads, or combinations of such loads, and where the maximum total voltage drop on both feeders and branch circuits to the farthest outlet does not exceed 5 percent, will provide reasonable efficiency of operation.
i found that and assumed it was a rule, we have to size for voltage drop up here so i assumed it would be the same. Seems silly not to follow it. At 800 feet to the pump who knows if it will even turn on.
Old 05-12-2012, 07:13 PM   #6
Electrical Contractor
jbfan's Avatar
Rewards Points: 386
Fine print notes are not a requirement, but a suggistion.
That's not to say you should'nt adjust, just not required.
The Following 2 Users Say Thank You to jbfan For This Useful Post:
andrew79 (05-13-2012), Code05 (05-12-2012)
Old 05-13-2012, 05:54 PM   #7
the well pump tag says 9 amps, the pump is 550 feet away from the barn and is a 300 ft submersible well pump, I have 8-2 wire run for the 550 feet to the well pump pressure switch and then 12-2 wire down the well to the pump
wire size question analogmusicman Electrical 8 09-01-2011 06:17 PM
What size ground wire should I use for 8 gauge power dxmullin Electrical 1 07-06-2011 02:57 PM
Question about neutral wire through wall switch guitarmonster Electrical 33 08-08-2010 09:51 PM
hooking up dryer....bronx ny code SURFBUG Appliances 6 10-14-2008 09:41 PM
Aluminum wire size/ guage / amps? walt1122 Electrical 17 07-30-2008 10:44 AM