wire size and OCPD in mixed phases


I've got a 3 phase 200amp 120/208v 4 wire + ground sub panel panel that will be supplying five 3 phase machines with an FLA of 7 amps each and 5 single phase machines at 120v with an FLA of 10 amps each. Totals would be 35amps and 50 amps respectively. I don't know how to plug in these mixed numbers into my wire calculation table.

http://www.electrician2.com/calculat...cpd_ver_1.html

I need to determine the minimum wire size needed and the appropriate OCPD to put in my main panel that will feed this sub described above. All the loads will be non continuous.

The 200 amp panel was the only size I could find with enough spaces to hold all the breakers.

thanks,
David

n175h is offline   Reply With Quote
Join DIYChatroom.com

Join the #1 DIY Forum Today - It's Totally Free!

DIYChatroom.com - Are you about to start a new home improvement task and need some help? Do you need advise on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that DIY Chatroom is a great community to join. Best of all it's totally free.

Join DIYChatroom.com - Click Here
JOIN FOR FREE


Warning: The topics covered on this site include activities in which there exists the potential for serious injury or death. DIYChatroom.com DOES NOT guarantee the accuracy or completeness of any information contained on this site. Always use proper safety precaution and reference reliable outside sources before attempting any home improvement task!
Old 01-27-2012, 11:04 PM   #2
Member
 
Join Date: Mar 2011
Location: Central Florida
Posts: 613
Default

wire size and OCPD in mixed phases


if the single phase loads are divided as equally as possible(2a, 2b, 1c, etc.), you'll have a maximum of 55A on one phase.

Techy is offline   Reply With Quote
Old 01-28-2012, 03:30 AM   #3
retired elect/hvac/plumb
 
plummen's Avatar
 
Join Date: Jan 2010
Location: south east of omaha
Posts: 2,391
Default

wire size and OCPD in mixed phases


How big is the main service ?
plummen is offline   Reply With Quote
Old 01-28-2012, 07:02 AM   #4
Licensed Electrical Cont.
 
Speedy Petey's Avatar
 
Join Date: Feb 2004
Location: NY State
Posts: 6,158
Default

wire size and OCPD in mixed phases


Quote:
Originally Posted by n175h View Post
I've got a 3 phase 200amp 120/208v 4 wire + ground sub panel panel that will be supplying five 3 phase machines with an FLA of 7 amps each and 5 single phase machines at 120v with an FLA of 10 amps each. Totals would be 35amps and 50 amps respectively. I don't know how to plug in these mixed numbers into my wire calculation table.

http://www.electrician2.com/calculat...cpd_ver_1.html

I need to determine the minimum wire size needed and the appropriate OCPD to put in my main panel that will feed this sub described above. All the loads will be non continuous.

The 200 amp panel was the only size I could find with enough spaces to hold all the breakers.

thanks,
David
This is obviously not a home improvement DIY job.
Hire a licensed, insured electrician.
__________________
Sometimes I feel like if I answer any more questions it is like someone trying to climb over a fence to jump off a bridge and me giving them a boost.
Speedy Petey is offline   Reply With Quote
Old 01-28-2012, 11:03 AM   #5
Member
 
Join Date: Dec 2011
Location: Livermore, California
Posts: 265
Default

wire size and OCPD in mixed phases


Quote:
Originally Posted by Speedy Petey View Post
This is obviously not a home improvement DIY job.
Didn't you hear? Converting your garage to a laundromat is the latest craze.
a_lost_shadow is offline   Reply With Quote
The Following User Says Thank You to a_lost_shadow For This Useful Post:
Speedy Petey (01-28-2012)
Old 01-28-2012, 08:38 PM   #6
Member
 
Join Date: Oct 2009
Location: South TX outside San Antonio
Posts: 148
Default

wire size and OCPD in mixed phases


Quote:
Originally Posted by a_lost_shadow View Post
Didn't you hear? Converting your garage to a laundromat is the latest craze.
You're right. No garage. It's on hold for now. I'm still waiting on the AEP load engineer to give my electrician a quote for a 3 phase changeover. However, for my own knowledge, I would like to know how to compute the wire size and OCPD for the load described in the original post.

Plummen, the main service will be 400a 120/208 3 phase.

Seems to me it would be 35 + 30 = 65 Three of the five 10 amp single phase machines would be on one 120v phase. I appreciate the knowledge shared on this forum even if it is above and beyond DIY

David

n175h is offline   Reply With Quote
Reply


-->
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Burial wire and a seeming difference of opinion... SxS Electrical 19 02-24-2009 10:16 AM


Top of Page | View New Posts


All times are GMT -4. The time now is 02:05 PM.


© 2003 - 2010 The Building Network LLC