Old 01-07-2013, 10:06 AM   #1
Wire size for generator
I ordered an 8000 watt Generac generator which has a 30 amp 240 volt outlet. I’m will be storing it in a shed out back and pull it out as needed. I’m going to run a PVC conduit from the inlet on the shed to the transfer switch in the garage. I also want to run a 20 amp. circuit in the same conduit for an outlet in the shed for a battery minder. The run from the shed will be 50 feet and the conduit will have, I believe 5 current carrying conductors in it. Do I need to go up to #8 wire for the generator and #10 for the outlet due to distance and/or derating?
Thank you
Bob972 is offline   Reply With Quote
Old 01-07-2013, 11:29 AM   #2
The #10 gauge wires will work perfectly well for 30 amps at 50 feet.
You might choose to put in 8 or even 6 gauge wires in case you might use a larger generator in the future. For those sizes the ground wire can still be #10.
The #12 wires will be fine for the 20 amp circuit. Again, you could use heavier wires and/or 3 wires on this circuit in case you may want to use more amperes or 240 volts out at the shed
The disadvantages of crab apple trees. In summer, the apples are too sour to pick and eat. In winter the birds come and leave dropping all over the place.
Old 01-07-2013, 12:21 PM   #3
Thank you for the quick reply. The other thing I wanted to mention is that I will be using a 10’ cord which would increase the distance to 60’. Would I still be okay with #10 gauge due to voltage drop? A 10 gauge cord would be easier work with. I don’t see go with a larger generator. If I did I would probably go with a whole house standby generator which would be placed in a different location. I might consider larger 3 wires possibly for 240 volts to the shed.
New Sub Panel Wire Size? johnsas Electrical 4 08-29-2012 12:20 PM
Ground Location and Wire Size LHB_Texas Electrical 25 05-27-2011 10:38 AM
wire size for 160' feeder to subpanel steveski Electrical 3 05-21-2011 10:41 AM
hooking up dryer....bronx ny code SURFBUG Appliances 6 10-14-2008 10:41 PM
Wire size and Breaker size for remodel ?? Skydmark1 Electrical 12 12-15-2007 06:00 PM