wire
I have some #10 type tw wire. Could I run 5 of these thru conduit from the control pannel about 6 feet to the pumps, 2 hots for each pump and one ground for both.Part of the conduit will be shared by both pumps. What size conduit? also what size and type of copper or aluminium cable could be used in place of the conduit and thwn in the basement and or underground ? In the basement it would be on the ceiling so I would not consider it subject to physical damage. and lastly what is the proper way to terminate the aluminium cable. thanks again!
WDR is offline   Reply With Quote
Old 08-06-2010, 11:00 PM   #17
UAW SKILLED TRADES
Stubbie's Avatar
Rewards Points: 2,652
#10 copper most likely would be fine ... tw however is a 60C wire insulation so the fuse blocks need to be rated for 60C or 60C/75C. In other words if the fuse blocks are rated 75C only you cannot terminate a 60C insulated wire to those fuse blocks.
Minimum conduit size for 5 tw #10's is 3/4" for all raceways.
I not familiar with any aluminum multiwire cable with outer sheath that would be applicable for direct burial.
You can use copper uf-b cable or copper power cable type TC or MC cable . I prefer type TC power cable.
" One nice thing about the NEC articles ... you have lots of choices"
Stubbie
Old 08-06-2010, 11:20 PM   #18
WDR
cable
what would you recomend for the main run including under ground and the basement section?
Old 08-06-2010, 11:37 PM   #19
UAW SKILLED TRADES
Stubbie's Avatar
You would need #4 aluminum in conduit to meet the ampacity requirements of the feeder. USE-2 al can be direct buried but would need to be in conduit above grade and the run to the panels.
I always recommend a conduit installation with individual copper conductors if length is not to excessive.
My second choice would be USE-2 using conduit above grade. Be sure your fuse block will accept the bigger wire.
My third choice would be power type TC copper cable 3 conductor with ground this will avoid any splicing in J boxes since it is direct bury rated..
Stubbie
Old 08-06-2010, 11:48 PM   #20
WDR
cable
I thing I will go with copper in a conduit as the run is fairly short. If I was to go with a nother method what would be the most affordable that you would recommend? and thank you very much for all of your help with this project.
Old 08-07-2010, 12:06 AM   #21
UAW SKILLED TRADES
Stubbie's Avatar
Power cable type tc you need to go to an electrical supply.
http://www.southwire.com/ProductCata...prodcatsheet69
You cannot use the 90C ampacity shown on the chart for you application
You could also use UF-b cable but the largest awg is #6 copper. This is a little under proper design specs but since your fuses are 60 amp you would likely be fine. UF-B #6 is 55 amp rated.
Stubbie
Old 08-07-2010, 12:32 AM   #22
WDR
tc cable
If I used tc cable would it need conduit? and what gauge would I need also do you know anywhere to get it near murphysboro, IL
Old 08-07-2010, 01:26 AM   #23
UAW SKILLED TRADES
Stubbie's Avatar
Nope no conduit required, treat it just like uf-b ... burial depth should be 24".
Any electrical supply has it or can order it in.
To comply with code and proper design and unknown terminal temperature ratings at the fuse box you will need #4 . However you say you can only install a max 60 amp fuse so if that doesn't change IMO you can use #6 at 55 amps 60C terminations. TC power cable is rated 90C but generally we use the 60C ratings for ampacity . Some will argue that TC can use 75C and 6 awg would then let you use 65 amps. Anyway IMO you will be fine with #6.
Stubbie
Old 08-07-2010, 07:09 AM   #24
WDR
fuse
#4 would be fine because the fuse terminals are rated up to #2 aluminum and #4 copper however one cable company I found online only has it up to #10 also if I was able to change the run and remove the underground pard could I use 2-2-2-4 type SER aluminum cable?
Old 08-07-2010, 10:18 AM   #25
UAW SKILLED TRADES
Stubbie's Avatar
Yes that would be fine if you do not bury it and do an overhead feeder to the pump house. IMO you want to use a wiring method that is continuous without splice from the basement fuse panel to the pump controller. It wouldn't hurt to have that feeder terminate in a disconnect at the pump house then to the controller ..in fact it is likely required. As is a grounding electrode.
Stubbie
Old 08-07-2010, 10:38 AM   #26
WDR
cable
I am not sure wich method I will use yet as it depends on which type of cable i can get. Thank you again, you have have been a great help!
Size and type of entrance wire for 200A? Beemer533 Electrical 7 03-15-2010 10:54 PM
HALP! Master/Remote Dimmer troubles! Confuserated Electrical 9 02-12-2010 03:30 PM
hooking up dryer....bronx ny code SURFBUG Appliances 6 10-14-2008 09:41 PM
What size wire do I have? 737Pilot Electrical 4 10-09-2008 09:47 PM
Wire size and Breaker size for remodel ?? Skydmark1 Electrical 12 12-15-2007 05:00 PM