Old 04-10-2008, 10:51 AM   #16
Electrical Contractor
Wire size and breaker discrepancy
Thank you gentleman for pointing out my error.
I was responding to the original post, namplate information 14 gauge, 20 amp breaker.
There are some instances that you can have a 20 amp breaker on 14 gauge wire, the code allows it (see table 310.16)(422.62(B)(1)), but is only for certain applications, and/or if the manufacture specifies it.
Not in this case. I contacted Nutone and they confermed that it was a misprint and this unit should be wired with 12 gauge wire.
hpp58 is offline   Reply With Quote
Old 04-10-2008, 12:25 PM   #17
UAW SKILLED TRADES
Stubbie's Avatar
I'm not understanding why they want this wired with 12 awg...? It only uses 11.5 amps (heater and fan combined) and is a dedicated requirement for the branch circuit. Theres nothing wrong with 12 awg but I don't see where it is a requirement based on a fixed appliance load.
Old 04-10-2008, 12:46 PM   #18
This whole thing is screwed up, and it starts with the nameplate information.
For me the amperage draw is very close to the 80% load limit on 14 gauge wire, and thats not counting the starting current of the motor. I would install the 12 gauge wire with a 20 amp breaker and not have to worry about it. This way the inspector doesn't shoot it down.
Old 04-10-2008, 01:17 PM   #19
Learning by Doing
Leah Frances's Avatar
I hate manufacturer 'mistakes' like the one you encountered. I bought a door latch that came with the 'wrong' template for cutting the holes. Thankfully, it was only off by an 1/8th and the decorative plate around the knob hid the problem. Seems a lot more trivial than messing up what gauge wire/breaker.
If I could only remember to THINK about what I was doing before I did it.
Leah Frances is offline   Reply With Quote
Old 04-10-2008, 01:19 PM   #20
When is fishing season?
CowboyAndy's Avatar
The question is, if a fire or something resulted from their misprint, would they be held responsable for it?
I DON'T OWN MY HOUSE...
MY HOUSE OWNS ME!
CowboyAndy is offline   Reply With Quote
Old 04-10-2008, 01:38 PM   #21
That's why you pull permits, and get inspections.
There's another set of eyes to help you out.
With 800 pages of the the NEC and who knows how many in the UCC, I don't want to tax my brain too much. I just keep the code book with me all the time so I can refer to it.
Old 04-10-2008, 05:22 PM   #22
Electrician
What 80% load limit? There is no such thing except continuous loads, which are far and few in residential.
chris75 is offline   Reply With Quote
Old 04-10-2008, 05:43 PM   #23
Can it run for three hrs?
Chances are it won't, but it could.
Anayway the manufacture specificies it for 12 gauge (as per my phone conversation today). Put it on a 20 amp breaker and we are done with it.
Old 04-10-2008, 08:03 PM   #24
nap
You talking to me?
nap's Avatar
hpp58
Again, you are wrong. Please explain how 422.62 B 1 would allow 14awg on a 20 amp breaker.
What that section states is the manufacturer can list the minimum AMPACITY (not size) of the supply conductor and the max OCPD allowed for the circuit. That does not mean they can tell you to use 14 on a 20 amp breaker. What they can tell you is they require a conductor that will carry a minimum of xx amps and the OCPD must not be greater than xx amps. That does not allow you to disregard the NEC and their limitations they impose on the conductors.
and to the continuous load rating and your statement of:
NEC defines a continuous load as one that is EXPECTED to run for 3 hours or more.
By your own statement, the appliance would not be a continuous load.
14 awg does not have a load limit of, what I believe you are referring to, 15 amps. Depending upon the type of wire used, it varies. thhn actually has a rating of 25 amps. The 80% you speak of would be concerning the OCPD which by code, is limited, except is a few situations, to 15 amps on a #14 wire.
stubbies post:
Yeah it appears to be a screw up...not all that uncommon. I posted the links to nutone and at the bottom it shows the specification sheet and installation guide.
The specifications sheet says connect to a dedicated 15 amp branch circuit.
The installation guide says in bold type to be sure to use a 20 amp branch circuit.
http://www.nutone.com/product-detail...roductID=10150
Ok, it does give different ampacities of circuits required but I could find nothing in either piece of literature that specified a wire of any size, let alone an incorrect wire size.
So randall, where did you get the wire size recommendation?
More On This Topic
Differences in Wire Gauges
Differences in Wire Gauges by Expert Village
Hello! This is Ross on behalf of expertvillage.com. Wire thickness is measured in gauge. The bigger the number, the smaller the wire. For instance, house wiring is commonly 14 gauge or sometimes might be 12 gauge if it needs to handle more current and it... Read More »
Even the smallest components of a high-end home audio system can influence overall sound quality. Many audiophiles like to argue about which types of connectors reproduce the best signal or what speaker angle is best for ideal sound coverage. However... Read More »
Basic Electrical Tools
Basic Electrical Tools by Expert Village
These are some of the tools that you may or may not need when you are doing your electrical ventures around the house. These are your snips, they're basically just metal shears. Your linesman pliers. Every electrician needs a crescent wrench. These are... Read More »
How to Use Wire Strippers
How to Use Wire Strippers by Expert Village
Hi! I'm Drew Finch here for Expert Village and we are talking about standard hand tools and how to use them. Now we are going to use a couple of basic tools to help strip some romex wire if you are doing any wiring. The first thing we have to do is get... Read More »
Hi! My name is Chad Smith and I'm a state certified Journeyman Wireman basically a electrician and I'm representing expertvillage.com. Today we are installing a new doorbell in our house here. The first step that you should take when you are installing... Read More »
Circuit breakers and wire size stan 41943 Electrical 19 03-06-2008 03:29 PM
Generator Safety Switch Help - Breaker Size? limey_swindon Electrical 3 01-09-2008 12:40 PM
Wire size and Breaker size for remodel ?? Skydmark1 Electrical 12 12-15-2007 06:00 PM
Wire size for distance Question fburke Electrical 4 07-28-2007 10:29 AM
wire size wire to 10kw furnace? lochcarron Electrical 1 04-10-2005 08:43 PM
Copyright ©2000 - 2010, Jelsoft Enterprises Ltd.