Old 04-09-2008, 02:29 PM   #1
Default Wire size and breaker discrepancy
I bought a Nutone bathroom heater/vent combo for a new install. The manufacturer's recommendation for the wire size and breaker is #14/3 on a 20 amp breaker.
I was under the impression that #14 was only rated at 15 amps. Are there some finer points I'm missing?
Randell Tarin is offline   Reply With Quote
Old 04-09-2008, 03:06 PM   #2
You are correct that a 20-amp circuit requires a circuit wired with #12.
Old 04-09-2008, 03:15 PM   #3
Electrical Contractor
For branch circuits 14 gauge wire can only get a 15 amp breaker.
For dedicated circuits you can use a 20 amp breaker with 14 gauge wire, see 240.4D,
hpp58 is offline   Reply With Quote
Old 04-09-2008, 04:01 PM   #4
hpp58,
Could you please elaborate? When I read 240.4(D) it says nothing about dedicated circuits and seems to me to state very clearly that 14 ga. is limited to 15 amps.
Old 04-09-2008, 05:13 PM   #5
This is a dedicated circuit.
Old 04-09-2008, 05:23 PM   #6
Licensed Pro
This is one of those instances where the manufacturer's recommendation is wrong. If it is a heater/vent (no light) you need to use 12/3 w/g on a 20A circuit. Using 14ga on a 20A is not permitted in this situation.
Old 04-09-2008, 06:14 PM   #7
UAW SKILLED TRADES
Stubbie's Avatar
Randy
More accurately 240.4(D) restricts the protection of 14 awg to a 15 amp circuit breaker in your case. 14 awg copper is rated at 20 amps (table 310.16). There are situations where you can put a 20 amp breaker on 14 awg copper however this heater/vent combo is not one of them.
What is the model#?
Old 04-09-2008, 06:34 PM   #8
Model No. 605RP
All the instructions say is: "Provide a separate 20 amp circuit. Use 14 GA power cable of type which meets code."
Sounded fishy to me.
Old 04-09-2008, 06:37 PM   #9
I'm new here, but some of this info being presented by so called "contractors" is poor at best. These DIYer's are going take this info without doing any credible research and take it as gospel.
Aren't there any moderators or whatever to watch out for this mis-information. This is very dangerous.
Joba Fett is offline   Reply With Quote
Old 04-09-2008, 06:49 PM   #10
UAW SKILLED TRADES
Stubbie's Avatar
Yeah it appears to be a screw up...not all that uncommon. I posted the links to nutone and at the bottom it shows the specification sheet and installation guide.
The specifications sheet says connect to a dedicated 15 amp branch circuit.
The installation guide says in bold type to be sure to use a 20 amp branch circuit.
http://www.nutone.com/product-detail...roductID=10150
Old 04-09-2008, 07:04 PM   #11
UAW SKILLED TRADES
Stubbie's Avatar
I should add that the unit operates at 11.5 amps total. The heater is 1300 watts which makes it 10.8 amps and the motor would be another 3/4 of an amp or so. Since this is fixed space heat the heater would require conductors rated 13.5 amps. So a 15 amp branch circuit will do the trick.
Old 04-09-2008, 07:07 PM   #12
Thanks Stubbie. I already had a roll of 14/3 I had bought for my smoke alarms. That saves me the expense of going out and buying 12/3 wire.
Old 04-09-2008, 08:06 PM   #13
Isn't this credible research? There are plenty of licensed electricians on the board that will catch and correct any "mis-information" that is posted.
--A conservative liberal
jerryh3 is online now   Reply With Quote
Old 04-09-2008, 10:13 PM   #14
nap
You talking to me?
nap's Avatar
while hpp58 did post incorrect information, it was caught and corrected by several others. There are also mods that do watch and correct when they do see a problem but many of the regulars here are electricians and do know the correct answers.
As a member of this forum, joba fett, if you see an incorrect post, you are hereby required to make a corrective post. As well, you may report that thread to the moderator who will look at the thread and attach their corrective post, if they believe it is needed.
and yes, electrical work is very dangerous. That is why most here do take it very seriously and do what they can to make sure correct info is provided.
Old 04-10-2008, 12:52 AM   #15
Electrician
THis is a misprint in their instruction manual, I've heard this one before...
chris75 is offline   Reply With Quote
More On This Topic
Basic Hot Tub Wiring
Basic Hot Tub Wiring by Expert Village
OK, here we're going to talk about the different wiring requirements for spas. Many spas, most common will be a two-forty volt, fifty amp dedicated circuit, which means that is it on its own breaker, it is a GFCI breaker which is for your safety and also... Read More »
Let's talk about putting a sign on the breaker box to warn others to avoid others turning our breaker back on. You can say something on your sign similar to what I have. Do not turn circuit breaker number 15 on. Bill is installing a dimmer switch in the... Read More »
Differences in Wire Gauges
Differences in Wire Gauges by Expert Village
Hello! This is Ross on behalf of expertvillage.com. Wire thickness is measured in gauge. The bigger the number, the smaller the wire. For instance, house wiring is commonly 14 gauge or sometimes might be 12 gauge if it needs to handle more current and it... Read More »
Making jewelry is a fun hobby that lets you make great accessories for yourself or give away exquisite gifts to your loved ones. To get started, you need to know how to find the right wire gauge for your project. If the wire is too big or too small, it... Read More »
Hi! This is John on behalf of Expert Village. In this video clip, I will show you Part 1 of replacing an old switch. First you need to locate your service entrance. This is where the electricity comes in and goes through your house. If you open it up... Read More »
Circuit breakers and wire size stan 41943 Electrical 19 03-06-2008 04:29 PM
Generator Safety Switch Help - Breaker Size? limey_swindon Electrical 3 01-09-2008 01:40 PM
Wire size and Breaker size for remodel ?? Skydmark1 Electrical 12 12-15-2007 07:00 PM
Wire size for distance Question fburke Electrical 4 07-28-2007 11:29 AM
wire size wire to 10kw furnace? lochcarron Electrical 1 04-10-2005 09:43 PM
Copyright ©2000 - 2009, Jelsoft Enterprises Ltd.