Wire Size? - Electrical - DIY Chatroom Home Improvement Forum
Old 10-26-2008, 01:34 AM   #1
wire size?
I need to run a underground line(in conduit) from my main box to a building approximately 150 feet away.
I planned on putting a 75 amp breaker in my main box and running the wire from it.
What size copper wire would be required?
LipCa is offline   Reply With Quote
Old 10-26-2008, 09:27 AM   #2
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,882
I am curious about something. Why are you choosing a "75 amp" breaker???
There is not even such a thing as a 75 amp breaker.
Answer this and we can answer your wire size question.
Old 10-27-2008, 12:29 AM   #3
Speedy...
If I knew anything about breakers, I wouldn't be asking about wire size...grin.
I "googled" 75 amp breaker and got dozens of references to 75 amp breaker:
Here's one:
ITE Pushmatic Circuit Breaker 75 AMP double pole
ITE Pushmatic Circuit Breaker 75 AMP double pole See more about 'ITE Pushmatic Circuit Breaker 75 AMP double pole'
Anyway, I will be using about 45-50 amps on the circuit(welder) plus some lights so I thought 75 should be good....
What would you suggest?
Old 10-27-2008, 12:46 AM   #4
This was from another forum:
I can give you what the National Electric Code Says;
14 ga 15 amp breaker
12 ga 20 amp breaker
10 ga 30 amp breaker
8 ga 40 amp breaker
6 ga 50 or 60 amp breaker
4 ga 75 amp breaker
3 ga 100 amp breaker
So if they really don't make a 75 amp breaker for my use, what do they make between 60 and 100?
Old 10-27-2008, 01:30 AM   #5
8 ga 40 amp breaker
4 ga 75 amp breaker
Usually 70,90 and then 100
(That chart is talking about copper, not aluminum. Thats a different story.)
rgsgww is offline   Reply With Quote
Old 10-27-2008, 01:34 AM   #6
DIYer
http://www.cerrowire.com/default.aspx?id=46
Gigs is offline   Reply With Quote
Old 10-27-2008, 06:56 AM   #7
Ampacity charts are one thing. Breaker sizes are another.
According to the NEC 75a is NOT a standard breaker size. I was just curious as to how you came to the decision to use that particular size. That was my point.
I agree. 70, 80, 90 or 100 amps. This fact dictates that you will need at least #4cu or #2al. The distance pretty much rules out 100a, so I would recommend a 70 or 80 amp feeder breaker.
Are you doing conduit the whole way or direct burial cable?
Old 10-27-2008, 12:40 PM   #8
If I had known 75 was not a common breaker, I would have selected 70 or 80.
I was just trying to select something above my uses.
It is 1.5" conduit all the way with correct number of sweeps.
Thanks for the info
hooking up dryer....bronx ny code SURFBUG Appliances 6 10-14-2008 10:41 PM
Aluminum wire size/ guage / amps? walt1122 Electrical 17 07-30-2008 11:44 AM
wire size greywolf6 Electrical 8 07-14-2008 10:08 PM
Wire size and Breaker size for remodel ?? Skydmark1 Electrical 12 12-15-2007 06:00 PM
wire size wire to 10kw furnace? lochcarron Electrical 1 04-10-2005 08:43 PM