Old 03-30-2008, 01:09 PM   #16
Idiot Emeritus
Wire size
Thanks, Marc. I'll write that down as a reference. Very handy when working with metric equipment.
In the above example, a 5.4 anp motor about 600' away, #8's would be my choice as well.
Rob
micromind is offline   Reply With Quote
Old 03-30-2008, 02:13 PM   #17
Cow
Wire size
Originally Posted by idoelectric View Post
#6 copper stranded is good for 30 amps at 120v for a distance of 500 ft.
I'm not sure where the 7 amps came from?
Cmils= 2 x K x I x D / VD
I believe you're mistaken. Use the formula you posted and see what you come up with. Unless you're shooting for 15% VD?
FYI, the 7 amps was calculated using this formula:
I=(CM x VD)/(2 x K x D)
Cow is offline   Reply With Quote
Old 03-30-2008, 04:45 PM   #18
My License Ain't 4 Sale..
Wire size
Originally Posted by elkangorito View Post
I don't know about the USA but calculating the voltage drop for a given cable length & current, is not a simple process in Australia.
I generally use the formula VD = (2KxIxD)/cm
where K is a typical value for the resistivity of copper, 12.9 ohms/cm-ft
I is the current
D is the distance, in feet
and cm is the circular mils of the wire.
I transpose the equation into cm = (2KxIxD)/VD
where VD is 3.6V for 120 V or 7.2 for 240 V.
So if I know the current, this tells me the wire size in circular mills. I can then select from a chart of standard gauges to the nearest size.
Our wire ampacities are selected from a table of based on what conditions the wire is used in. Most typically, it is based on no more than 3 conductors in a conduit of cable, or directly buried in earth. There are other tables for free air and other conditions.
InPhase277
Circuit breakers and wire size stan 41943 Electrical 19 03-06-2008 03:29 PM
Wire size and Breaker size for remodel ?? Skydmark1 Electrical 12 12-15-2007 06:00 PM
Wire size for distance Question fburke Electrical 4 07-28-2007 10:29 AM
Wire size for Central Air mwtuck HVAC 2 12-01-2006 06:06 PM
wire size wire to 10kw furnace? lochcarron Electrical 1 04-10-2005 08:43 PM