Wire Size For 1500 Watt Baseboard Heater - Electrical - DIY Chatroom Home Improvement Forum
Old 03-15-2011, 09:19 PM   #1
wire size for 1500 watt baseboard heater
I'm installing a baseboard heater and thought I should probably use No. 12 wire and a 20 amp breaker. Am I right? Thanks.
beech is offline   Reply With Quote
Old 03-15-2011, 09:40 PM   #2
Master Electrician
Rewards Points: 3,678
What voltage?
brric is offline   Reply With Quote
Old 03-15-2011, 09:42 PM   #3
120 volts
Old 03-15-2011, 09:45 PM   #4
Master Electrician
Yes, use 12-2 with ground.
The Following User Says Thank You to brric For This Useful Post:
beech (03-15-2011)
Old 03-15-2011, 09:46 PM   #5
Thanks Bud
Old 03-16-2011, 01:53 PM   #6
Here I am again. My wife just found a wall hung heater rated 1000w with a boost to 2000w. It is 240 v. Will 12-2 wire be sufficient or should i use 12-3. Should I use a 40amp double pole breaker? Hope I'm right. Thanks
Old 03-16-2011, 02:08 PM   #7
CodeEnforcer
HIVOLT's Avatar
Rewards Points: 99
12/2 is still fine and use a 20A 2 pole breaker.
HIVOLT is offline   Reply With Quote
The Following User Says Thank You to HIVOLT For This Useful Post:
beech (03-16-2011)
Old 03-16-2011, 06:13 PM   #8
I=E/R
a7ecorsair's Avatar
The reason you can still use 12-2 is because watts are watts and you will be wiring this heater at 240 volts.
Power = voltage X Current. The power remains the same but because the voltage doubled, the current will be 1/2.
Circuits powering in place heaters are sized at 80% so:
120 volts X 20 amps (12 ga wire) = 2400 watts X 80% = 1920 watts
240 volts X 20 = 4800 watts X 80% = 3840 watts
You could actually do it with 14 ga wire
240X15=3600 X 80% = 2880 watts
a7ecorsair is offline   Reply With Quote
The Following User Says Thank You to a7ecorsair For This Useful Post:
beech (03-16-2011)
Pilot on Williams millivolt wall heater goes out every 8 to 16 hours wornways HVAC 30 06-22-2011 04:29 PM
Problem with 240V Elect Baseboard Heater JRHP Electrical 4 10-04-2010 10:30 AM
wire size for ac/heating forced air unit macfluke Electrical 2 03-04-2009 01:29 AM
Baseboard heater Help! jweinstock Electrical 6 10-28-2006 05:01 PM
wire size wire to 10kw furnace? lochcarron Electrical 1 04-10-2005 08:43 PM