Originally Posted by Knucklez View Post
the NEC tables are conservative.. there is a lot of wire in those cables.
Ummmm.......WHAT??
...there are also derating factors such as duty %, load type etc..
Ummmm.......WHAT??
...but generally you don't fill your panel more than 80% (80Amps)
Ummmm.......WHAT??
Speedy Petey is online now   Reply With Quote
Old 06-18-2011, 07:30 PM   #17
Me thinx kbsparky in wrong column. THHN is rated 90 C not 75 C; and thus, 115 according to 2011 NEC Code Table 310.15(B)(16) formerly 310.16. It can be confusing with all the types of wire.
Coqui is offline   Reply With Quote
Old 06-18-2011, 07:33 PM   #18
Electrical Contractor
kbsparky's Avatar
Not quite. You can not use the 90 degree column for final connections unless you have equipment terminations rated at that temperature.
All the breaker box manufacturers that I am aware only have their terminations rated at 75 degrees, thus you are limited to wire with that capacity/rating.
You can start with the 90 degree ratings before any adjustments are made for things like ambient temperature and conduit fill deratings, but your final figure is restricted to the 75 degree values or less.
-KB
The Following User Says Thank You to kbsparky For This Useful Post:
Coqui (06-19-2011)
Old 06-18-2011, 07:45 PM   #19
Knucklez's Avatar
Rewards Points: 932
what i mean is.. the 12 gauge wire can take more than 20Amps.. before it has any problems. but your local code does not allow it, so this is what i mean by conservative.
duty %, i am refering to that not all the loads are on at any one time. for instance, a 100A panel with 30 slots, even if they were all just 15 Amp breakers, would be 450Amps. obviously the idea is that not all the breakers will be on giving full power to the load. so this is what i mean by duty.
not filling more than 80%, i am refering to CEC (i don't know if it is in NEC) where it talks about if you don't know what the load is, then don't fill more than 80%. that is just from memory.. section 8, part I.
didn't mean to lead anyone astray..
"if you can't be handsome, at least you can be handy" -Redgreen
Knucklez is offline   Reply With Quote
Old 06-18-2011, 07:47 PM   #20
kbsparky's Avatar
You posted this in the wrong thread, knucklez
-KB
Old 06-18-2011, 07:50 PM   #21
Aside from the fact that we are talking about NM cable, which is limited to the 60 deg C column.
Old 06-18-2011, 08:03 PM   #22
kbsparky's Avatar
No we weren't. As stated previously, you can't get #3 in NM cable. This part of the discussion is definitely about #3 THHN/THWN.
-KB
Old 06-19-2011, 06:28 PM   #23
kbsparky and I are on #3 THHN we dropped the Romex #2/3 line of inquiry.
The Following User Says Thank You to Coqui For This Useful Post:
Speedy Petey (06-19-2011)
What size wire to use running underground ms66cadillac Electrical 21 01-13-2011 11:14 AM
What size wire do I need? walnut777 Electrical 1 12-13-2010 06:41 PM
Sub-Panel Wire Size and Conduit Questions Tmb9862 Electrical 3 12-02-2009 11:48 PM
Size of Wire & type of wire agman Electrical 6 11-10-2009 08:13 PM
Aluminum wire size/ guage / amps? walt1122 Electrical 17 07-30-2008 10:44 AM