Wire Size To 100 AMP Subpanel - Electrical - DIY Chatroom Home Improvement Forum
Old 06-16-2011, 09:10 PM   #1
Wire size to 100 AMP subpanel
Looking for the correct 3 conductor w/ ground wire size from 100 AMP breaker in service panel to my 100 AMP subpanel. Romex size vs. THHN size using conduit. What is the benefits of one over the other?
Coqui is offline   Reply With Quote
Old 06-16-2011, 09:18 PM   #2
Electromagician
one advantage to conduit and thhn is that I have never seen romex that size before.
powerfactor is offline   Reply With Quote
Old 06-16-2011, 09:51 PM   #3
Electrical Contractor
kbsparky's Avatar
I doubt you will be able to find romex large enough to handle 100 amps. #2 is listed in Southwire's catalog, with a 95 Amp rating. I suppose you could special order a reel of the stuf, but it will probably be cost prohibitive.
#3 THHN in conduit, with a #8 ground (if using PVC) is sufficient for 100 Amps.
IF you upsize to #2 THHN, you may be required to upsize your ground to a #6.
-KB
Old 06-17-2011, 01:13 AM   #4
Thanks. You are correct that #2/3 Romex is only rated 95 AMPs, but my town issued a permit to me with this as an option. I was a little uncomfortable, after reviewing the 2011 NEC code, because the Romex did not meet 100% of the ampacity rating. The advice gave me the reassurance to go with THHN #2 w/ #4 ground.
Old 06-17-2011, 03:35 AM   #5
Rewards Points: 1,192
Howzabout 3 #2W/g M.C. cable? I like it.
bobelectric is offline   Reply With Quote
Old 06-17-2011, 05:55 AM   #6
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,992
Originally Posted by Coqui View Post
Thanks. You are correct that #3/2 Romex is only rated 95 AMPs,.........
Which is typical and fine for a 100A sub-feeder. There is no such thing as a 95A breaker so we round up to 100A.
So you went oversized on both?
What 125% ampacity rating are you referring to?
The Following User Says Thank You to Speedy Petey For This Useful Post:
electures (06-17-2011)
Old 06-17-2011, 11:50 PM   #7
Electromagician
sorry but 3/2 romex is only rated for 85 amps.
Old 06-18-2011, 06:35 AM   #8
Lic Electrical Inspector
electures's Avatar
Rewards Points: 1,108
It also need to be three conductors plus a ground.
electures is offline   Reply With Quote
Old 06-18-2011, 10:24 AM   #9
Thumbs up
I read #3/2 to be a typo for #2/3 and I inadvertantly followed the typo in my response, for which I apologize and corrected above. Anyone reading this thread should understand that we are not talking about two conductors but three conductor (two hots, one neutral, and the ground). Romex NM-B #2/3 is rated 95 Amps. I went back and reviewed the NEC Code and changed my decision to that recommended by kbsparky (THHN #3, which is rated 115 Amps, with a #6 ground (#8 is the minimum and acceptable). This was extremely helpful, thanks.
The Following User Says Thank You to Coqui For This Useful Post:
Speedy Petey (06-18-2011)
Old 06-18-2011, 11:15 AM   #10
Uhhhh..yup. Me too.
Old 06-18-2011, 02:09 PM   #11
kbsparky's Avatar
...I went back and reviewed the NEC Code and changed my decision to that recommended by kbsparky (THHN #3, which is rated 115 Amps....
Ummm ... #3 THHN is rated for 100 Amps not 115, if you use the 75 degree column listed in table 310.16 of the NEC.
#2 is rated for 115 Amps.
Me thinx your typos are still haunting you ...
-KB
Old 06-18-2011, 02:28 PM   #12
Electromagician
so is it three twos or two threes and are we using a single two or is it a three? nevermind I will go back and edit an old post to throw the threads whole context off.
Old 06-18-2011, 02:47 PM   #13
kbsparky's Avatar
Thought I'd catch you in a quote before you edit it ...
AFAIK, there ain't no such thing as 3/2 romex. SouthWire makes it in #4, then #2 ... skipping #3 altogether. Click here for the list, and scroll down to page 2. #3 ain't on the chart.
-KB
Old 06-18-2011, 03:35 PM   #14
Electromagician
check post number two. but don't quote it as I may want to edit it!
Old 06-18-2011, 06:54 PM   #15
Knucklez's Avatar
Rewards Points: 942
the NEC tables are conservative.. there is a lot of wire in those cables. #3 is fine. there are also derating factors such as duty %, load type etc.. but generally you don't fill your panel more than 80% (80Amps) so a 100A rated cable is just fine.
"if you can't be handsome, at least you can be handy" -Redgreen
Knucklez is offline   Reply With Quote
What size wire to use running underground ms66cadillac Electrical 21 01-13-2011 11:14 AM
What size wire do I need? walnut777 Electrical 1 12-13-2010 06:41 PM
Sub-Panel Wire Size and Conduit Questions Tmb9862 Electrical 3 12-02-2009 11:48 PM
Size of Wire & type of wire agman Electrical 6 11-10-2009 08:13 PM
Aluminum wire size/ guage / amps? walt1122 Electrical 17 07-30-2008 10:44 AM