Wire Requirements For 15 Amp 205 Volts - Electrical - DIY Chatroom Home Improvement Forum
Old 10-07-2010, 03:46 PM   #1
Rewards Points: 272
wire requirements for 15 amp 205 volts
I am installing a heater in my garage it is rated at 15 amps with 205 volts. Do I need 14 gauge wire or 12 gauge wire?
fixrite is offline   Reply With Quote
Old 10-07-2010, 05:21 PM   #2
Civil Engineer
Rewards Points: 4,856
Required wire size for under 600 volt appliances is determined by the amperage. In your case, 15A could in theory work with 14 gage, but I always use 12 gage and put in a 20A breaker. You will save a few cents with 14 gage, but you are right at code limit.
By the way, I have never heard of a 205 volt appliance. Where are you planning to get 205 volt service?
Old 10-07-2010, 05:37 PM   #3
Rewards Points: 272
I went with 12 gauge wire and a 15 amp double poll as it is 208 volts 2500 watts. It is a heater that I bought online from Vanoc ( Vancouver Olympic committee) it was brand new in the box. It is an INFRATECH heater made in the USA. It also states on the wiring diagram that it is 240 Volts A/C 3600 watts max,15 amps max.
Old 10-07-2010, 05:37 PM   #4
nap
You talking to me?
nap's Avatar
Rewards Points: 6,290
because of the voltage, you have a problem. As Daniel stated, there is no such voltage supply as 205 volts. Due to that, you need to verify the required voltage of the heater.
Old 10-07-2010, 05:39 PM   #5
Rewards Points: 272
I am taking the readings right off of the sticker on the heater itself. It states 208 volts,2500 watts.
Old 10-07-2010, 05:41 PM   #6
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,974
Fixed electric heating is required to be figured at 125% of the load, so #14 on a 15A breaker will not suffice.
IF the actual load is 15A you can and should use 12/2 on a two-pole 20A breaker.
Speedy Petey is online now   Reply With Quote
Old 10-07-2010, 05:41 PM   #7
nap
You talking to me?
nap's Avatar
well, 208 volts is not 205 but besides that;
what is your supply voltage in the building you are installing this?
Old 10-07-2010, 05:42 PM   #8
That changes things. I for one would not use a 208V heater in a 240v application. Others might.
Old 10-07-2010, 05:42 PM   #9
nap
You talking to me?
nap's Avatar
pete, he has a 208 volt rated heater. If he has 240 volts supply, he cannot (legally) hook it up to his supply.
Old 10-07-2010, 05:43 PM   #10
Besides, 2500 watts @ 208v is 12 amps.
Old 10-07-2010, 05:43 PM   #11
Rewards Points: 272
Seems the paper work and the sticker on the appliance are not saying the same thing, so I will have to check this out further.
Old 10-07-2010, 05:44 PM   #12
I didn't see that before I posted. I was a few minutes behind. I had to go away from my desk and then I posted.
Old 10-07-2010, 05:56 PM   #13
nap
You talking to me?
nap's Avatar
ya. every time I posted, I would come back and something else was added. Just kind of cross posting.
It's all cool. this way the OP gets the point...X2.
Old 10-07-2010, 06:10 PM   #14
Wire Chewer
Red Squirrel's Avatar
Rewards Points: 132
I would contact the manufacturer and ask if it will handle 240 volts ok. You may be able to do it but it will draw more amps but probably not much more then what it's rated for. I'd use 12/3 with a 20 amp breaker, just to future proof that circuit for either another heater later on,or other appliance that may need the neutral too.
Old 10-07-2010, 06:12 PM   #15
nap
You talking to me?
nap's Avatar
Red Squirrel;513128]I would contact the manufacturer and ask if it will handle 240 volts ok.
legally that is not acceptable. You cannot hook up an appliance to a voltage it is not rated for. A manufacturer would be foolish for saying it's ok. The liability would be horrendous.
ROMEX 14-2 wire from Canada Vs. ROMEX 14-2 wire from the U.S. Dazzlin Electrical 18 11-02-2016 03:15 PM
Tripping breakers,neutrals,120 volts and 240 volts OH My!!! Stubbie Electrical 17 06-11-2011 06:09 AM
Adding ground in old home ChaosTheory Electrical 6 06-16-2010 04:02 PM
Is using a ground wire as neutral wire safe? Head Fred Electrical 9 12-18-2008 02:37 PM
Old house, new light fixture, too many wires Persephonee Electrical 3 01-15-2007 08:58 AM