Old 09-23-2010, 01:12 PM   #1
Member
 
kevinp22's Avatar
 
Join Date: Sep 2010
Location: Saint Louis, MO
Posts: 323
Share |
Default

wire gauge on afco 20a breaker


just installed a 20a cutler hammer CH series AFCI breaker in my house, just noticed that the wire gauge on the breakers pig-tail to the neutral bar is only 14 AWG stranded.

Seems odd to have 14 as part of a 20A breaker, but i know this is acceptable in certain circumstances. Asked 2 home depot electricians and they were perplexed - it was reassuring to have them point out it was a UL listed device. One thought it might be a manufacturing defect, but we opened another in the store and found the same thing.

Any thoughts?

thanks
kevin

kevinp22 is offline   Reply With Quote
Old 09-23-2010, 02:11 PM   #2
Member
 
Join Date: Oct 2009
Location: Indiana, PA
Posts: 1,282
Default

wire gauge on afco 20a breaker


thats wierd, I just bought a 15 amp GE AFCI breaker and it had 12 gauge stranded wire for the pigtail

BlueBSH is offline   Reply With Quote
Old 09-23-2010, 02:12 PM   #3
DIY'er
 
jamiedolan's Avatar
 
Join Date: Sep 2008
Location: Neenah, Wisconsin, USA
Posts: 2,032
Blog Entries: 2
Default

wire gauge on afco 20a breaker


Quote:
Originally Posted by kevinp22 View Post
just installed a 20a cutler hammer CH series AFCI breaker in my house, just noticed that the wire gauge on the breakers pig-tail to the neutral bar is only 14 AWG stranded.

Seems odd to have 14 as part of a 20A breaker, but i know this is acceptable in certain circumstances. Asked 2 home depot electricians and they were perplexed - it was reassuring to have them point out it was a UL listed device. One thought it might be a manufacturing defect, but we opened another in the store and found the same thing.

Any thoughts?

thanks
kevin
Devices that are UL listed / approved do not have to comply with the same standards as everyone else does that needs to follow the NEC. For example, wires in fixtures are often smaller than the gage that the NEC would specify for the circuit they will be installed upon.

It is also such a short wire that even if you put a 20A load on a 14 gage wire that short, it would not be likely to get over the temp rating for that piece of wire.

I am not sure how exactly the AFCI's work and if that wire carries current or if it is more for sensing.
__________________
Jamie Dolan - Neenah, WI
Jamie Dolan Paw Dogs
Need Help Uploading Photos? Click here.
jamiedolan is offline   Reply With Quote
Old 09-23-2010, 02:15 PM   #4
Member
 
Join Date: Oct 2009
Location: Indiana, PA
Posts: 1,282
Default

wire gauge on afco 20a breaker


Quote:
Originally Posted by jamiedolan View Post
Devices that are UL listed / approved do not have to comply with the same standards as everyone else does that needs to follow the NEC. For example, wires in fixtures are often smaller than the gage that the NEC would specify for the circuit they will be installed upon.

It is also such a short wire that even if you put a 20A load on a 14 gage wire that short, it would not be likely to get over the temp rating for that piece of wire.

I am not sure how exactly the AFCI's work and if that wire carries current or if it is more for sensing.
the neutral pigtail on the AFCI breaker is the neutral return for the entire circuit... to wire an AFIC you connect the hot and neutral to the breaker (2 screws on the breaker) then pigtail goes to the neutral bus
BlueBSH is offline   Reply With Quote
Old 09-23-2010, 02:22 PM   #5
Licensed Electrical Cont.
 
Speedy Petey's Avatar
 
Join Date: Feb 2004
Location: NY State
Posts: 6,772
Default

wire gauge on afco 20a breaker


The conductor is also not in a cable or conduit, so it could be considered in free air.


Quote:
Originally Posted by kevinp22 View Post
...............Asked 2 home depot electricians and they were perplexed - ..................
PLEASE don't tell me you are referring to the store employees.

99.9% of them are FAR from electricians.
Speedy Petey is offline   Reply With Quote
Old 09-23-2010, 02:24 PM   #6
Member
 
kevinp22's Avatar
 
Join Date: Sep 2010
Location: Saint Louis, MO
Posts: 323
Default

wire gauge on afco 20a breaker


I am not sure the NEc code reference (310.1.6?) but I think the answer is that 14 AWG single coductors "open air" which this would be can handle 20A, but in a cable with other conductors it is limited to 15A

thanks for all the helpful and quick replies
kevinp22 is offline   Reply With Quote
Old 09-23-2010, 02:27 PM   #7
Member
 
kevinp22's Avatar
 
Join Date: Sep 2010
Location: Saint Louis, MO
Posts: 323
Default

wire gauge on afco 20a breaker


i use 2 home depots, one of which has a "master electrician" licensed since 1988 - his face and hours and picture are even up on the wall in the dept. Others have experience "working as electricians" in the past but are out of work due to the economy.
kevinp22 is offline   Reply With Quote
Old 09-23-2010, 02:30 PM   #8
Licensed Electrical Cont.
 
Speedy Petey's Avatar
 
Join Date: Feb 2004
Location: NY State
Posts: 6,772
Default

wire gauge on afco 20a breaker


Quote:
Originally Posted by kevinp22 View Post
i use 2 home depots, one of which has a "master electrician" licensed since 1988 - his face and hours and picture are even up on the wall in the dept.
This guy is likely in that .1% I mentioned.

Quote:
Originally Posted by kevinp22 View Post
Others have experience "working as electricians" in the past but are out of work due to the economy.
These guys, not so much.
Speedy Petey is offline   Reply With Quote
Old 09-23-2010, 05:53 PM   #9
DIY'er
 
jamiedolan's Avatar
 
Join Date: Sep 2008
Location: Neenah, Wisconsin, USA
Posts: 2,032
Blog Entries: 2
Default

wire gauge on afco 20a breaker


Quote:
Originally Posted by Speedy Petey View Post
PLEASE don't tell me you are referring to the store employees.

99.9% of them are FAR from electricians.
I had one (at home depot wih his photo on the wall as the store electrician) that claimed he was a liceansed electrician, but said he is retired.

He insisted I was going to "Burn my house down" by running 6 circuits (3 - MWBC) in a piece of EMT. He said each circuit still counts as 2 conductors even in a MWBC. So he claimed 3 MWBC counted as 12 CCC.

He also explained how I can get my power "cheaper" by balencing out the load on my panel. He said if both legs are equal they cancel eachother out and I won't get charged anything for the power I use.

Didn't he directly contradict himself with these 2 statements that were both bogus to begin with......

__________________
Jamie Dolan - Neenah, WI
Jamie Dolan Paw Dogs
Need Help Uploading Photos? Click here.
jamiedolan is offline   Reply With Quote
Old 09-23-2010, 07:33 PM   #10
Member
 
Join Date: Oct 2009
Location: Indiana, PA
Posts: 1,282
Default

wire gauge on afco 20a breaker


Quote:
Originally Posted by jamiedolan View Post
I had one (at home depot wih his photo on the wall as the store electrician) that claimed he was a liceansed electrician, but said he is retired.

He insisted I was going to "Burn my house down" by running 6 circuits (3 - MWBC) in a piece of EMT. He said each circuit still counts as 2 conductors even in a MWBC. So he claimed 3 MWBC counted as 12 CCC.

He also explained how I can get my power "cheaper" by balencing out the load on my panel. He said if both legs are equal they cancel eachother out and I won't get charged anything for the power I use.

Didn't he directly contradict himself with these 2 statements that were both bogus to begin with......


sounds like someone who misunderstands how AC current works
BlueBSH is offline   Reply With Quote
Old 09-23-2010, 07:36 PM   #11
I=E/R
 
a7ecorsair's Avatar
 
Join Date: May 2010
Location: Minnesota
Posts: 2,052
Default

wire gauge on afco 20a breaker


Quote:
Originally Posted by jamiedolan View Post
He also explained how I can get my power "cheaper" by balencing out the load on my panel. He said if both legs are equal they cancel eachother out and I won't get charged anything for the power I use.

Didn't he directly contradict himself with these 2 statements that were both bogus to begin with......

I need to talk to this guy so I can figure out how to connect my neutrals to the meter so my power will be free
a7ecorsair is offline   Reply With Quote
Old 09-23-2010, 07:42 PM   #12
I=E/R
 
a7ecorsair's Avatar
 
Join Date: May 2010
Location: Minnesota
Posts: 2,052
Default

wire gauge on afco 20a breaker


Somehow it posted twice

Last edited by a7ecorsair; 09-23-2010 at 07:44 PM. Reason: posted twice
a7ecorsair is offline   Reply With Quote
Old 09-23-2010, 07:57 PM   #13
" Euro " electrician
 
frenchelectrican's Avatar
 
Join Date: Apr 2006
Location: WI & France { in France for now }
Posts: 5,369
Default

wire gauge on afco 20a breaker


Quote:
Originally Posted by jamiedolan View Post
I had one (at home depot wih his photo on the wall as the store electrician) that claimed he was a liceansed electrician, but said he is retired.

He insisted I was going to "Burn my house down" by running 6 circuits (3 - MWBC) in a piece of EMT. He said each circuit still counts as 2 conductors even in a MWBC. So he claimed 3 MWBC counted as 12 CCC.

He also explained how I can get my power "cheaper" by balencing out the load on my panel. He said if both legs are equal they cancel eachother out and I won't get charged anything for the power I use.

Didn't he directly contradict himself with these 2 statements that were both bogus to begin with......

James.,

Which one the east side or west side of big orange ??

If on West side watch your rear end { I am not going to comment on how bad it was but they learn a hard way from moi.}

Merci.
Marc
frenchelectrican is offline   Reply With Quote
Old 09-23-2010, 11:10 PM   #14
DIY'er
 
jamiedolan's Avatar
 
Join Date: Sep 2008
Location: Neenah, Wisconsin, USA
Posts: 2,032
Blog Entries: 2
Default

wire gauge on afco 20a breaker


Quote:
Originally Posted by frenchelectrican View Post
James.,

Which one the east side or west side of big orange ??

If on West side watch your rear end { I am not going to comment on how bad it was but they learn a hard way from moi.}

Merci.
Marc
Yes It was the west store. Not sure if the same guy is stll there or not, last I saw of him was maybe a year ago or more. I've been getting electrical stuff at Werner lately, better prices than HD on most stuff anyway.

From a discount / cleareance area, I picked up a 1" x 18" lenox auger from werner for $10. I grabbed a 1.5" x 18" also for the same price.

__________________
Jamie Dolan - Neenah, WI
Jamie Dolan Paw Dogs
Need Help Uploading Photos? Click here.
jamiedolan is offline   Reply With Quote
Reply

Tags
14 awg, afci


Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
GFCI Breaker Tripping Spa Light eaposition Electrical 21 09-08-2010 09:57 PM
12 volt kitchen cabinet lighting wire gauge? Help! :/ Lupinglade Electrical 16 09-25-2009 11:55 AM
Standard gauge for household electrical wire tripower Electrical 2 09-21-2008 11:42 PM
Wire gauge recommendations please Snowdog Electrical 33 08-22-2008 03:54 PM
Gauge Wire and Breaker Discrepancy broken_scout Electrical 26 12-22-2007 10:07 PM




Top of Page | View New Posts

Copyright © 2003-2014 Escalate Media. All Rights Reserved.