Wire Gauge For 80 Amp Continues Load - Electrical - Page 2 - DIY Chatroom Home Improvement Forum
Old 11-27-2012, 05:19 PM   #16
kbc1's Avatar
Originally Posted by diyguy41
That is a good point about the 12/2 vs 10/2 in the receptacles I could route things to run 4,200 watts per circuit which is around 18 amps I was just concerned about bumping up to the 85% rule. On the flip side, that has to be a little on the conservative side, no?
One last question, what size PVC conduit am I looking at in order to run two #3 and a #6 wire. Is that 2"? It is a 24 foot run with a 90 degree bend on each end. Not going to be terribly fun I imagine
More fun that cutting an egress window in my 110yo foundation. Did that last year. Not messy at all LOL
Thanks again guys!
i would use 1-1/4 make it more easier, also why not run a couple of smaller pvc pipes while you have a trench for future phone , tv, etc.....
kbc1 is offline   Reply With Quote
Old 11-27-2012, 09:37 PM   #17
Semi-Pro Electro-Geek
Rewards Points: 2,970
Originally Posted by Glennsparky View Post
Maximum breaker for #12 NM (NM-B/Romex) is 20A. Since he needs a 25A breaker. It's either upsize the NM or use a different wiring method.
And, does somebody have a code book? What's the de-rating at 94 degrees?
Good point. Even though I mentioned it recently, I didn't put 2+2 together. He'll need #10 wire and 30A breakers (25 if he can find them, but not likely). That also makes the 15A receptacles noncompliant. He'll need to hard-wire the lights or use 30A rated connectors (twist-lock probably).
I am a lawyer, but not your lawyer. And who cares anyways? We're here to talk construction. This is DIY advice, not legal advice.
mpoulton is offline   Reply With Quote
Old 11-27-2012, 11:09 PM   #18
" Euro " electrician
frenchelectrican's Avatar
Originally Posted by mpoulton View Post
You shouldn't need #10 wire for 20A circuits. These runs aren't likely to be long enough for voltage drop to require up-sizing the conductors, so #12 is fine. You also shouldn't need delays between lamp startups, since the 80% load factor provides plenty of overhead and most lighting doesn't have a significant startup surge. If the greenhouse is not attached to the garage, then you need to put the new panel in the greenhouse, not in the garage. If it's attached to the garage then having the panel and other equipment in the garage instead of the greenhouse is probably better since it spares the equipment from humidity. Greenhouses are very hard on electrical equipment. But If the greenhouse is IN the garage, then the plants probably aren't "ornamental"...
In OP's situation if they want to keep 20 amp circuit you have to derated them to 16 amp which that is 80% right there and the only time I used the word " continous " if the load will stay on 3 hours or more then the derating do kick in.
Merci,
Marc
Old 11-28-2012, 11:35 AM   #19
Rewards Points: 204
Originally Posted by stickboy1375 View Post
Because all the OP's loads are 240volts, you are not required to run a grounded conductor (neutral) to a sub-panel.
You are saying 3 wire sub panels are compliant?
I am asking. Why would anyone set a sub panel with a 3 wire feeder?
I know it would be a four wire feeder if I was installing it.
Even with a 120 volt service, you still have the grounded conductor.
Old 11-28-2012, 11:48 AM   #20
TTW
TTW's Avatar
I would run the Neutral so I had a 120 volt outlet to plug in the radio. It makes the plants happier (as long as you don't play heavy metal).
TTW is offline   Reply With Quote
Old 11-28-2012, 12:30 PM   #21
E2 Electrician
stickboy1375's Avatar
The service is required to have a grounded conductor run. After that point though, if all my loads are line to line, what is the purpose to have a grounded conductor to a sub panel?
Generator to transfe switch wire gauge Kirk5291 Electrical 3 07-18-2012 11:31 AM
Ceiling fan and wire gauge needs? greentrees Electrical 6 05-01-2012 01:05 AM
efficiency voltage drop wire gauge jackwashere Electrical 6 02-18-2012 08:33 PM
What Gauge Wire do I need? rjrivero Electrical 23 11-03-2011 04:11 PM
Standard gauge for household electrical wire tripower Electrical 2 09-21-2008 11:42 PM