whip wires're rated for 600f according to the markings,,, i'm buying line to the jct box, NOT for inside the stove at the junction block.
yes.itsconcrete is offline   Reply With Quote
Old 09-10-2008, 10:19 PM   #17
UAW SKILLED TRADES
Stubbie's Avatar
Rewards Points: 2,652
Ok then 8/3 G NM to the jb if the whip is 3 wire with ground. Any chance you could share a picture of what you have at the breaker box end?
Old 09-11-2008, 05:12 AM   #18
8/3 G NM ? ? ? stub, wtf're you talkin' about ? ? ? can figure out the 8/3 as being #8 wire & 3 of them but G NM ??? told you i wasn't fluent in electrical
yesitsconcrete is offline   Reply With Quote
Old 09-11-2008, 07:28 PM   #19
8/3 = 3 #8's (red, black, white)
wg = with ground (bare #10)
NM = non metalic cable (Romex)
8/3 wg NM = a theromplastic sheathed cable containing 3, #8 insulated wires and a bare #10 typically used in residential construction to provide a 40 amp 240 volt circuit for ranges and double ovens.
^Not for use in Chicago
I know.....I just get sidetracked telling stories.
220/221 is offline   Reply With Quote
Old 09-11-2008, 08:14 PM   #20
thanks for the translation, 220,,, by the time stub's signed back on, i'll be in beddy can you believe some kitchen guy quoted $65K for 25' of cabinets & some other stuff ? ? ? the price of concrete's going UP !!!!!!!!!
seriously, i DO appreciate all your collective help,,, know it was a walk-in-the-park post but i don't want my casa burning down.
Old 09-11-2008, 10:39 PM   #21
Rewards Points: 81
Stubbie: I am confused as to why 8 guage wire is needed, if its 2 hot wires and 40 amps total shouldn't that be 20 amps on each hot wire, meaning it should have 12 gauge wire?
daxinarian is offline   Reply With Quote
Old 09-11-2008, 11:20 PM   #22
UAW SKILLED TRADES
Stubbie's Avatar
The circuit breaker serving as the protection for the branch circuit conductors to his double oven is a 40 amp double pole.
Old 09-12-2008, 02:37 AM   #23
Electrical Contractor
kbsparky's Avatar
Nope. 40 Amps on each hot wire = 40 Amp breaker.
And while using a #8 AWG conductor is acceptable, there are instances where a #10 wire on a 30 Amp breaker would be sufficient in such installations. It all depends on the rated wattage of the appliance.
Old 09-12-2008, 08:50 AM   #24
Rewards Points: 81
Originally Posted by yes.itsconcrete View Post
twin 20s stack'd together w/common throw bar printed ' 40a ',,, who knows where the ovens' manuals are ? ? ?
Could you clairify this? Do you have two 20 amp breakers tied together or two 40 amp breakers tied together?
Old 09-12-2008, 10:06 AM   #25
if you're talkin' to me, dax, yes - its 2 20a breakers tied together,,, if you're talkin' to my newest best friend, stub - who knows ? ? ?
Old 09-12-2008, 10:42 AM   #26
Rewards Points: 81
Stubbie and KBSparky: this is a 20 amp double pole breaker, not a 40 amp, it should only require 12 gauge wire not 8 gauge.
Last edited by daxinarian; 09-12-2008 at 10:44 AM. Reason: (original post sounded snarky which wasn't my intent)
Old 09-12-2008, 05:35 PM   #27
kbsparky's Avatar
Sheesh, go back and read the OP's description in message #5 in this thread. Better yet, here it is:
... YUP, 2 twenty amps and a handle tied 40,,, you been down in my basement ? ? ?
That describes what is commonly known as a "quad" breaker, which in this case has 2 single pole 20 Amp breakers on the outsides, and a double 40 Amp breaker in the center. The whole assembly takes up 2 full size spaces in the panel box. If you click here, you can see an example of a similar breaker with a double 50 sandwiched between 2 single 20's.
The OP stated that the circuit was originally wired with Aluminum wire, probably a #8. He wants to replace that with copper. A good idea IMO.
IF he wants to use that breaker, then he has to use at least a #8 wire for the circuit to the oven.
My question has yet to be answered: What is the name-plate wattage of the oven? In many circumstances, such an oven would be adequately served with a #10 wire and a 30 Amp overcurrent protection.
Old 09-12-2008, 05:54 PM   #28
wish i could post a photo,,, these're TWO 20a breakers side-by-side w/common handle imprinted ' 40 amp ',,, even expect its ONE unit fitting into 2 slots,,, said i was barely fluent in electrical but if you understand english, that's all they iz
gawda'mighty, all's i asked was what size wire,,, didn't mean to start a skirmish.
the ovens' plates are gone or in hiding,,, even if i were to use #6 wire, i'd still be safe, tho.
Old 09-12-2008, 07:10 PM   #29
Just get a wood burning oven.
You are likely misreading the "20 amp" part.
Old 09-12-2008, 09:11 PM   #30
& eat pizza & flat bread for the rest of my life ???
for all of YOUR sakes, i got the following off the ovens' tag - 120v/240v - 8.6Kw ---- 120v/208v - 6.5Kw
how difficult can it be to misread ' 20 amp ' on each breaker & 40 amp on the ' common breaker handle ' ? ? ?maybe i can't SPEAK electrical but i can still READ it
Aluminum wire size/ guage / amps? walt1122 Electrical 17 07-30-2008 10:44 AM
wire size greywolf6 Electrical 8 07-14-2008 09:08 PM
Wire size and Breaker size for remodel ?? Skydmark1 Electrical 12 12-15-2007 05:00 PM
Wire size for distance Question fburke Electrical 4 07-28-2007 09:29 AM
wire size wire to 10kw furnace? lochcarron Electrical 1 04-10-2005 07:43 PM