-   -   wire connection (http://www.diychatroom.com/f18/wire-connection-179604/)
hidden1 05-14-2013 11:23 PM
wire connection
152 Attachment(s)
Has anyone ever seen a #12 coming in to main panel box and both neutral an black coming in to hot side ,breakers are seperated by other ones, is on 2 different tandom circuits 20 amps. .I know white should be neutral but unsure on this set up.
Any info is appreciated.
AllanJ 05-15-2013 05:42 AM
That branch circuit should be a 240 volt only circuit.
Both ends of the white wire should be marked with colored tape or stain to indicate that it is not a neutral.
The up to date code requires that both the black and white be connected to breakers next to each other (or a double wide double breaker) with handles tied together so if one trips then the other is flipped off.
hammerlane 05-15-2013 06:17 AM
2 Attachment(s)
Originally Posted by hidden1 (Post 1179669)
I know white should be neutral.
You do not know what you say you know. Electricity does not care what color the conductor insulation is.
But as Allan mentioned if that white conductor is an ungrounded conductor(meaning a hot wire) then it needs to be reidentified with black tape or markings at its ends.
Maybe provide a photo of your situation
Philly Master 05-15-2013 09:17 AM
things that make you go HMMMM ....
MTN REMODEL LLC 05-15-2013 09:35 AM
Philly... I'm not sure I agree with all aspects of our codes (not restricted to just electrical)
... but seems identyfying a hot white with tape and tieing MWBC (and 240's) together at both the breakers and at panel entrance seem to be just good and inexpensive common sense to me.
I get those Hmmmmmmmmmmmmm's alot on rework.:huh:
Peter
Jim Port 05-15-2013 11:30 AM
Typically the tandem breaker only grabs one of the hot legs for both circuits. This would only give you 120, not 240 if both the black and white were attached to the breaker. GE has an arrangement where the breakers can be offset by 1/2 space and will grab both legs.
If a tandem is used to feed a MWBC it is quite possible that the neutral could carry up to 2x the neutral current.
MTN REMODEL LLC 05-15-2013 11:38 AM
Jim... on another thread I swore I had seen that pup.....a tandum that grabbed both phases... is GE only maker to your knowledge
Peter
sirsparksalot 05-15-2013 11:55 AM
Two posts for same problem? http://www.diychatroom.com/f18/wire-connection-179610/
Jim Port 05-15-2013 12:35 PM
And 2 posts about feeding the sump pump too.
