Wire In Conduit - Electrical - DIY Chatroom Home Improvement Forum
Old 04-11-2010, 08:13 AM   #1
wire in conduit
Hi I want to run 40 ft of 3/4 conduit with 4 curcuits 9 outlets in my garage I have lots and lots of 12/3 house wire can i strip off the white sheath cover and run it throught metallic conduit .Do I have to use a covered ground or is the bare ok or do I have to use the thhn wire
silver 11 is offline   Reply With Quote
Old 04-11-2010, 08:43 AM   #2
Electrical Contractor
jbfan's Avatar
Rewards Points: 490
The wire inside the romex is not rated to be used outside the cable jacket.
Any reason you can not use the romex to wire the garage?
jbfan is online now   Reply With Quote
Old 04-11-2010, 09:00 AM   #3
the walls are all block and I have a large roll of 12 /3 can i put the romex inside the metallic conduit with the sheath
Old 04-11-2010, 11:18 AM   #4
Rewards Points: 168
Buy the right wire and save the NM for another project.
Old 04-11-2010, 11:41 AM   #5
Its better to buy individual wires - easier to pull
You can use the 12-3 in conduit as long as it does not go outside or underground at all
You will probably need larger conduit since it is cable
1/2" is needed for (1) cable...not sure how easy that would be to pull
For (2) cables you would need 1"
Old 04-11-2010, 01:40 PM   #6
You CANNOT strip off the out coating and run the bare wires inside the conduit.
You CAN use the entire 12/3 inside the conduit so long as the conduit is not outside or underground.
And as scuba_dave also mentioned.... that is going to be a PITA to pull so.... if you have other projects to do later on... maybe just want to use the THHN (or THWN if the conduit will be outside or underground).
DownRiverGuy is offline   Reply With Quote
Old 04-11-2010, 03:24 PM   #7
thank for your hep I will run THHN wire. Can I use the same ground and netural for 3 circuits. that will be 3 #12 black 1 #12 green ground and 1 #12 white netural in 1/2 in or 3/4 metal conduit
Old 04-11-2010, 03:36 PM   #8
A "Handy Husband"
rjniles's Avatar
Rewards Points: 4,216
You can use a common ground but not a common neutral. You need 3 whites for the neutrals. You could make 2 of the hots a MWBC (multt-wire branch circuit) that shares a neutral, and get away with 2 whites. Personally I would not as it can sometimes make GFCI circuits difficult. One more run of THHN is not going to break the bank. And you do need GFCI protection in your garage.
Coastal South Carolina
Old 04-11-2010, 08:20 PM   #9
Unhappy
Just to enhance your point. The price of a 2-pole GFI breaker (if MWBC) will way offset the savings in pulling an extra Neutral wire! (Because One, or Two single pole GFI breakers won't work.)!
spark plug is offline   Reply With Quote
What type wire to use from transfer switch to outdoor outlet brjl Electrical 32 11-20-2013 08:36 AM
Sub-Panel Wire Size and Conduit Questions Tmb9862 Electrical 3 12-02-2009 11:48 PM
Mixing 12 and 14 wire in conduit? Quickdraw Electrical 80 04-19-2009 11:24 AM
Conduit for #6 wire joey b Electrical 13 11-22-2008 12:13 PM
adding new outside outlets, lights etc walt1122 Electrical 8 08-23-2007 02:11 PM