Hi guys, I recently purchased a hot tub wihich is name plated at 50amps(seems typical for most now even though this is a lower end model). Based on the math it maxes out at a bit less than 40 amps with everything on at once. Here's my dilema, the cable from the outside GFCI panel to the area where the hot tub will be has been prewired with #8/3 UFB. I still have to run the cable from the panel in my house to the GFCI panel as well as terminate the UFB at the tub and run sealtite to the ub panel. The UFB insulation is rated at 90C. If I use terminations at both ends rated at 75C can I use this on a 50 amp circuit? Assuming that my wiring from my main panel to the GFCI and the UFB termination to sealtite to the tub are rated 50amp?
HutchNJ is offline   Reply With Quote
Old 02-01-2013, 10:13 AM   #2
Rewards Points: 742
You're going to have to replace that cable anyway. UF cable is not permitted for outside wiring to a Spa.
Mark
busman is offline   Reply With Quote
The Following User Says Thank You to busman For This Useful Post:
jbfan (02-01-2013)
Old 02-01-2013, 10:29 AM   #3
If the UF cable comes out of the ground in PVC to a box why can't I run sealtite with individual wires to the hot tub panel?
Old 02-01-2013, 10:38 AM   #4
Rewards Points: 742
680.21. 2005 NEC. I don't have the 2011 with me.
Mark
Old 02-01-2013, 10:52 AM   #5
Sparky
Rewards Points: 510
Mark
Same article in 2011.
680.21 Motors.
(A) Wiring Methods.
The wiring to a pool motor shall com-
ply with (A)(1) unless modified for specific circumstances by
(A)(2), (A)(3), (A)(4), or (A)(5).
(1) General. The branch circuits for pool-associated mo-
tors shall be installed in rigid metal conduit, intermediate
metal conduit, rigid polyvinyl chloride conduit, reinforced
thermosetting resin conduit, or Type MC cable listed for the
location. Other wiring methods and materials shall be per-
mitted in specific locations or applications as covered in
this section. Any wiring method employed shall contain an
insulated copper equipment grounding conductor sized in
accordance with 250.122 but not smaller than 12 AWG.
The ground in UF Cable is bare, not insulated. Therefore not compliant.
Techy is offline   Reply With Quote
The Following User Says Thank You to Techy For This Useful Post:
J. V. (02-01-2013)
Old 02-01-2013, 11:13 AM   #6
Thanks for all your help. Looks like some rework. Last question, what is the max distance the GFCI disconnect can be from the tub. I know it's no closer than 5ft but I see a lot of different answers on the max.
thanks
Old 02-01-2013, 03:46 PM   #7
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,948
thanks
You probably won't find a maximum quoted, but typically within sight and/or 50' is a rule of thumb.
Old 02-01-2013, 07:06 PM   #8
I don't mean to beat this to death but this seems like UFB is suitable. This from NEC 2005 section 680.42.
any of the
wiring methods recognized in Chapter 3 of this
Code that contain a copper equipment
grounding conductor that is insulated or enclosed within the outer sheath of the wiring method
and not smaller than 12 AWG shall be permitted to be used for the connection to motor,
heating, and control loads that are part of a self-contained spa or hot tub or a packaged spa or
hot tub equipment assembly." What do you guys think?
Old 02-01-2013, 07:49 PM   #9
Licensed Electrician
k_buz's Avatar
Rewards Points: 2,006
What code cycle are you on? If you don't know, at least tell us what state you are located in.
Old 02-01-2013, 07:51 PM   #10
New Jersey
Old 02-01-2013, 08:02 PM   #11
k_buz's Avatar
New Jersey is on the 2011 code cycle so you are out of luck on the UF. The ground must be insulated.
As a word of warning. There are a multitude of codes concerning hot tubs...from needing a GFI receptacle to equipotential bonding grid. Since water and electricity do not mix well, I HIGHLY suggest you consult a licensed electrician, pull a permit, and have it inspected. A hot tub isn't something you simply wire up like an AC compressor.
The Following User Says Thank You to k_buz For This Useful Post:
Jim Port (02-01-2013)
Old 02-01-2013, 08:07 PM   #12
Licensed electrician
Rewards Points: 1,472
Article 680.42(c) applies to the interior portions of the circuit. Outside needs an insulated ground.
NJMarine (02-04-2013)
Old 02-01-2013, 08:45 PM   #13
UAW SKILLED TRADES
Stubbie's Avatar
Rewards Points: 2,652
UFB can only be used under the 60c column of table 310-16 for ampacity which is in your case 40 amps. Can't use the ampacity under the 75C column or the 90C column which is used for derating ampacity purposes.
I'm not sure what "based on the math means' ? Your wire ampacity must meet the nameplate electrical requirements of the spa.
Old 02-01-2013, 08:49 PM   #14
UAW SKILLED TRADES
Stubbie's Avatar
any of the
You forgot the subsection title .....
(C) Interior Wiring to Outdoor Installations.
In the interior
of a one-family dwelling or in the interior of another
building or structure associated with a one-family dwelling,
any of the wiring methods recognized in Chapter 3 of this
Code
that contain a copper equipment grounding conductor
wiring method and not smaller than 12 AWG shall be permitted
to be used for the connection to motor, heating, and control
packaged spa or hot tub equipment assembly. Wiring to an
underwater luminaire shall comply with 680.23 or 680.3
Old 02-04-2013, 07:03 AM   #15
Thanks again guys,
I'll verify this with my locality but in the short term here's my plan,
For a 50amp circuit to the hot tub I'll run #6 NMB inside my basement then a JBox to individual #6 conductors in PVC and flex under my deck structure to my GFCI panel then individual #6 conductors in metal conduit underground to the tub. (metal conduit so I only have to go 6in undersground and to go much more than that around here is difficult)
wiring a whirlpool cooktop davidtyson Electrical 8 06-17-2012 01:58 AM
magnet wire ampacity bizybily Electrical 2 11-04-2010 09:54 PM
6/3 wire through smurf tube? anygren Electrical 13 08-14-2010 07:23 AM
replacing 3 wire to 4 wire compressor fan - please advise! frazwr01 HVAC 2 06-27-2010 10:44 AM
hooking up dryer....bronx ny code SURFBUG Appliances 6 10-14-2008 09:41 PM